Hi all

After a little help please, as just completed my NVQ and AM2 and not completely confident in everything as I have only done one domestic job in my 4 year apprenticeship.
My neighbour has purchased a dual range cooker (7.4kW) and has asked if I can fit. After having a look I found this and was wondering if I am correct in what I have said:
They have had an extension and have a sub board with a 40A Rcd main switch feeding 32a mcb-skts and 6a-lights. The mains cable feeding this is 6mm SWA 3core. Obviously the range cooker would need its separate circuit so the board would need to be changed as its only a 4way but the mains cable feed would also need to be changed to at least 10mm SWA?
The neighbours plan was to go straight from the board through a wall which the range will be backed onto and terminated direct. Can't find anything in regs saying you can't terminate direct rather than through a cooker switch but is it best practice to do this?

thanks
 
If you can back entry to the cooker, then you can back entry into a switch and back out again to the cooker.
Saves running a round the house looking for the MCB when the chip pan is on fire. (do people still use chip pans?)

Seems pointless upgrading both the board and the cable, you might just as well run a new cable for the cooker from the main Consumer unit.
 

Reply to Dual range cooker in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
814

Similar threads

  • Question
Thanks for replying
2
Replies
23
Views
2K
  • Question
I actually did it with a 4 core 4.0mm swa last week!
Replies
12
Views
784

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top