Can anyone explain to me, if a 17th Edition Dual 30mA RCD board, is installed, with an earth rod (TT installation), why there is a need for a 100mA RCD to protect the whole installation?

Its something that l can't quite get my head round and would like someone to make things a little clearer.

Im aware that both 30mA RCDs are for electric shock protection, which would surely activate the event of an earth fault, so why have a 100mA RCD as well?
 
it's not required, used to fit 100mA RCD on TT systems because the Ze was so high, but now fitting 30mA RCDs to all circuits negates the need for the 100mA.
 
the only other reason for the installation of a 100 ma RCD or time delayed 30 ma RCD would be if the cable was installed in such a way it required additional protection by the RCD , but as Tel has said
 
Up front 100mA required on tails if the cu is metallic. Can still use 100mA on certain final circuits depending on installation methods.
 
100ma rcd was used for the lighting circs 30ma for sockets,thers a diagram in the iee sparks guide to building regs tho theres a split 30ma diagram thats labelled for all installations,no real need for 100ma as tel and nick say
 
100ma rcd was used for the lighting circs 30ma for sockets,thers a diagram in the iee sparks guide to building regs tho theres a split 30ma diagram thats labelled for all installations,no real need for 100ma as tel and nick say

Perhaps not used much in a domestic installation but 100mA RCD's are still commonly used in commercial and industrial installations.
 
Perhaps not used much in a domestic installation but 100mA RCD's are still commonly used in commercial and industrial installations.

agree mate,every tt ive seen has a 100ma rcd main switch even those with a new split dual 30ma rcd board fitted tho all these 100ma rcds are stand alone units with the tails to the new cu,tho do you have to use a 100ma rcd main switch for metal cu's ,im not 100% sure to be honest
 
Thanks, I have no doubt he is right. I am assuming it is to do with ensuring proper protection in case of an earth fault on on the input to the CU but I was wondering if there is a specific reg or whether it is just application of the normal fault protection rules.

EDIT: Don't worry, found it- 531.4.1
 
Last edited by a moderator:

Reply to Earth rod - rcd protection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
931

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
717

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top