Don't get me wrong I'm not trying to pull your work apart just for the sake of it but instead offer contructive advice, it seems where you have gone wrong here IMHO is you have let the cart lead the horse - so to speak, your customer can tell you what he wants and how he wants until the cows come home but it is up to you to tell him the options and limitations of his preferences.
As for plastic exposed outside - I would be taking a second thought before using it especially where both ends of any run may be to fixed points .
As for alterntives - well a few spring to mind:-
Externally
- cable of choice is a MICC with appropriate colour sheath (A dying or lost art) or a tough shell flex with UV tolerance.
- a stiff but flexible conduit with liquid tight glands.
- Plastic or steel conduit with the appropriate no' of expansion joints but such a set up would probably warrant an agreed inspection routine of say every few years to reseal all joints to keep them IP rated and if steel then ensure you use the IP rated fittings/joints.
I have also resued a few installs and my method seems to work so could be implemented from the start - Use PVC as you have but fit a 200mm piece of suitable flexible UV tolerant plastic flexible conduit in any runs especially the exposed runs ensuring the use of IP rated fittings - these act like and expansion joint but should reduce any movement on the fixed points thus compromising seals is limited.
PS - Look at these or similar and also read this link as it explains in detail the suseptibility of PVC to expansion
http://0323c7c.netsolhost.com/docs/Conduit expansion fittings.pdf