3 months ago I sunk in 3 rods, two were 4m deep and the other 3m deep, Ra achieved at the time was 3.1 ohms using a Three lead spike test kit.

i hooked the summerhouse up today and finished it off,

i measured Ra again and it was 2.5 ohms, then just to let you know how close it was to Ze, so accuracy of the spike test, Zdb at the new board came out at 2.88 ohms, that was on the end of a 52m run of 16mm SWA.

im very happy with the end result.

[ElectriciansForums.net] Earth rod[ElectriciansForums.net] Earth rod[ElectriciansForums.net] Earth rod
 
Last edited:
That did follow with not always glue them but often I do. To be honest glueing them just makes life difficult for you when you want to change the setup a bit.

Again, seriously?

What the hell is going to stop the whole lot falling apart if you don't glue it? It's an obvious failure to correctly erect the wiring system so a basic failure to comply with the regulations.
 
Again, seriously?

What the hell is going to stop the whole lot falling apart if you don't glue it? It's an obvious failure to correctly erect the wiring system so a basic failure to comply with the regulations.
seriously how will it fall apart if you dont glue it?

i wouldnt think the conduit would shrink more than 20mm between boxes?
 
seriously how will it fall apart if you dont glue it?

i wouldnt think the conduit would shrink more than 20mm between boxes?

Expansion and contraction will depend on how much the temperature changes and what temperature the conduit was at when it was installed.

There are other things which can cause it to fall apart. Natural movement of the structure it is fixed to or bumps and knocks can cause it.
 
Expansion and contraction will depend on how much the temperature changes and what temperature the conduit was at when it was installed.

There are other things which can cause it to fall apart. Natural movement of the structure it is fixed to or bumps and knocks can cause it.
fair enough, normally i would prefer black steel conduit rather than plastic if i needed to install it outside
 

Reply to Earth rod in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
461
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top