Earth wire on domestic heating oil tank - various questions

Hi all

I had a new consumer unit fitted 3 - 4 years ago. I was never told that I had to periodically test the RCDs by pressing the T buttons. Still, you live and learn!

Anyhow, it is a split unit. The left side tripped when I hit the button. But the right side didn't. Did a bit of reading but could figure it out. Until today. I remembered that when the unit was fitted the electrician also added an earth to our domestic heating oil tank, but this had become detached. I've re-attached it and hey presto, the RCD now works when tested.

So I thought I'd better check in with you guys....

1. Does it sound right that having the earth disconnected would have stopped the RCD tripping on being tested, and re-attaching would fix it?

2. What kind of connector is it (see picture below)? When I put the earth cable into the holes, the RCD wouldn't trip. When I out it into the gap and made sure it was touching the rod, it DID work and the RCD tripped when tested. So how should the cable be connected properly to that piece?

3. Just for my curiosity, why is the oil tank earthed?

4. Do I need to somehow cover that earth point/rod so that the dogs can't get to it, people don't trip on it etc?

Here are the pics:

Cheers

Max

IMG_1149 Small.JPG

IMG_1150 small.JPG

IMG_1154 small.JPG
 
That's why I said total lack of understanding..... chances are the pipework wasn't extraeneous to start with due to sheathing and a plastic bund. that is until the sparky made it so !

So you wouldnt bond that buried oil pipe because it has a plastic covering? What happens when the plastic gets damaged or breaks down and the pipe is then extraneous?! Rediculous.. bond it!
 
So you wouldnt bond that buried oil pipe because it has a plastic covering? What happens when the plastic gets damaged or breaks down and the pipe is then extraneous?! Rediculous.. bond it!

But he hasn't bonded it. He's earthed it with a rod. Daz.
 
If it's not bonded at the other end and connected to the MET then earthing it via its own rod could cause issues in the equipotential zone of the main installation. Also, connecting it via bonding to the MET could be an issue if the installation earthing arrangement isn't PME'd by the DNO.
 
If the oil pipe is bonded in the house then the earth rod connected @ tank end is not creating a danger nor has it any use, classic example of somebody doing something without knowing why or what there trying to achieve.
 
That's funny because on TT systems I often say the conductor to the rod is doing just that, earthing the rod. Take it away it will probably make no difference.
 
So you wouldnt bond that buried oil pipe because it has a plastic covering? What happens when the plastic gets damaged or breaks down and the pipe is then extraneous?! Rediculous.. bond it!

I would bond at the point of entry to the property I would not Earth it with an earthrod. My suggestion is that the addition of the earth rod has more than likely made the installation less safe
 
I would connect the bonding rod to an adjacent earthing rod. Belt and braces. In fact I'd earth my braces to be sure.
 