Ian1981

-
Mentor
Arms
V.Nearly Esteemed
Joined
Sep 22, 2016
Messages
3,786
Reaction score
4,073
Location
North east
Need someone either confirming or someone to put me right!
Regulation 551.4.3.2.1
Protection by ADS shall not rely upon the connection to the earthed point of the system for distribution to the public when the generator is operating as a switched alternative.
A suitable means of earthing shall be provided.

To me this means when the generator becomes the main source of power to the installation, then the generator TNS earthing arrangement shall not be connected to the DNO supply authority earthing arrangement,say it’s pme arrangement.
Am I correct?
 
It’s just an argument I’m having with an ‘electrical designer/engineer ‘ on a job I’m on.
I say a link needs to disconnect the generator earthing from the dno arrangement when the changeover switch is utilised.
He says I am wrong.
I’m thinking it could be near impossible. consider 4 industrial units, all with a seperate DNO supply, common steel frame , all bonded ect ect , you have a backup generator how can you disconnect all there earthing connections
 
Morning all - this is something im currently looking into but don't have much experience in myself.

To clarify; Does the mains earthing arrangement need to be switched in the changeover switch to a TT system when the generator is used as the mains supply?

Everyone I have spoken to has only ever seen 3pole + switched neutral change over switches so I'm unsure of what is the best way to complete the works.
 
I think post 5 sums it up. You must not rely on the DNO supply for an earth when using the genny, but probably don't need to disconnect it either. Ask the DNO.

to a TT system when the generator is used as the mains supply?

Having an earth rod at the genny doesn't make it TT. The earth terminal of the genny is referenced to real earth by the rod but the installation MET connects to that terminal by a cable, which makes it TN-S. Fault current from the installation flows through the cable, not the rod. It would only be TT if the genny had a rod and the installation had a rod, and the only connection between the two was the mass of earth, which is daft.
 
Just to add that often generators have output RCD in case they are used with sockets (stand alone supply) but also often to make sure they disconnect quickly as the PFC on a real fault from the generator is going to be far short of the grid's capacity. It that context they look a little like a TT supply, but as @Lucien Nunes points out, really are TN-S.
 
BS7430 is the reference for this - a genny servicing a building should be connected to that building's MET.
 

Reply to Earthing arrangements to a generator and change over switch in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

Similar threads

  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
1K
I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic
Replies
3
Views
925

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top