You can quote the relevant sections of such a document, or post an image of the appropriate section. But you can't post big chunks of the book like whole pages
 
Reg 543.2.7...where the protective conductor is formed by metal conduit, trunking or ducting or the metal sheath and/or armour of a cable, the earthing terminal of each accessory shall be connected by a separate protective conductor to an earthing terminal incorporated in the associated box or other enclosure.

Not too sure this reg' actually covers the OP's situation, the main switchgear and or distribution equipment isn't classed as an accessory like equipment tapped of each circuit would be IMHO, I did think of this reg' myself but decided it wasn't for this situe'.
 
Not too sure this reg' actually covers the OP's situation, the main switchgear and or distribution equipment isn't classed as an accessory like equipment tapped of each circuit would be IMHO, I did think of this reg' myself but decided it wasn't for this situe'.


How come you wouldn't class it as the same situation?
 
How come you wouldn't class it as the same situation?

Just checking the definitions in the BYB and it seems they have either revised the wording or I'm mixing my regs up as I don't just sit under the BS7671 in my job, so I'll stand corrected on that point, this regulation is applicable although I would argue the case that if you can effectively show you have taked the steps to ensure good solid contact and your not going through gland plates or screwed panelling and the earthing bolt/bar is fixed and grounded to the enclosure directly then you can argue by construction the gland doesn't require a tail.
I think the regulation is too broad in its application but like I said 'If in doubt, tail it out'
 
Last edited by a moderator:
Thank you i=p/u
As the supply is 150, I will probably use a 70mm, but as previously said the ohmic value between the points is 0.01, which suggests to me no 'tail' required. Then you have regulations to contend with. What I was trying to assertain is whether I could use a 35mm as the ohmic value was so low anyway. End of the day whatever I use to 'comply with regs' will just be a cosmetic price of cable, and just a complete waste of time and materials. That said a tail needs (and will) be installed.
 
How did you arrive at the value of 70mm

Just because the resistance is 0.01 ohms it does not mean it will handle the fault current safely.
You could measure the resistance of a short piece of 1.0mm T&E and get the same result, but it sure as hell won't cope with the fault current
 

Reply to Earthing inside a submain panel from main swa incomer in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
597
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
2K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top