This still will not answer my OP.
FYI the supply cable is FP600, so please post the relevant docs.
Reg 543.2.7...where the protective conductor is formed by metal conduit, trunking or ducting or the metal sheath and/or armour of a cable, the earthing terminal of each accessory shall be connected by a separate protective conductor to an earthing terminal incorporated in the associated box or other enclosure.
Not too sure this reg' actually covers the OP's situation, the main switchgear and or distribution equipment isn't classed as an accessory like equipment tapped of each circuit would be IMHO, I did think of this reg' myself but decided it wasn't for this situe'.
How come you wouldn't class it as the same situation?
I was referring to GN8 Appendix B (page 161)
This still will not answer my OP.
FYI the supply cable is FP600, so please post the relevant docs.
I was referring to GN8 Appendix B (page 161)