^ take a day off Dave, and go and read some books.

What's the problem?
I am trying to help you see why getting a low reading is not necessarily proof that you have a suitable path for the fault current.

If I was being unhelpful I'd have pointed out that your use of the term 'ohmic value' is somewhat wrong
 
OK guys n girls, first take a look at the table posted below

https://www.dropbox.com/s/820yq4v3l2zj1m8/swa_armour.pdf?dl=0

You can clearly see that a thermoplastic swa (FP600) of 150mm does not require a supplymentary earth.

Now with this FP600 Terminated directly onto the panel, and not through a gland plate, to me this termination is sound, and can handle any fault current. The R1R2 of the cable is 0.01 ohms back to the supply, tested at the gland. This same value is obtained from the earthing terminal inside the panel.

Hope this makes things clear.
 
OK guys n girls, first take a look at the table posted below

https://www.dropbox.com/s/820yq4v3l2zj1m8/swa_armour.pdf?dl=0

You can clearly see that a thermoplastic swa (FP600) of 150mm does not require a supplymentary earth.

Now with this FP600 Terminated directly onto the panel, and not through a gland plate, to me this termination is sound, and can handle any fault current. The R1R2 of the cable is 0.01 ohms back to the supply, tested at the gland. This same value is obtained from the earthing terminal inside the panel.

Hope this makes things clear.

A table on a page title DIY isn't going to carry much sway with anyone!
Plus that is not for the type of cable that you have, FP600 is a different spec to standard PVC SWA and so you need to get the CSA of the armour from the manufacturer.
But then nobody has questioned the suitability of the armour as a cpc, I think we all know that there are very few situations where an additional cpc is required.

If you are confident that the termination is suitable for the fault current then why did you ask the question in the first place?

If you have a good solid connection from the gland to bare metal then yes it may well be good enough, but a simple low current resistance test won't confirm this.
You are presumably dealing with a significant PFC on a cable that size and so I would have thought a little bit of belt and braces wouldn't hurt to ensure that fault currents will be handled safely.
 
Why you getting so upset? You've had useful reply's to your OP you just seem to be ignoring them or taking them out of context. Simply you have to size it using the adiabatic equation or use the table in the BYB. Are you incapable of performing a simple calculation or something as you seem to be trying to avoid it?
 
I'm not angry at all, I have tried to explain things as best I can.
I don't think I have tried to belittle you at all have I?
You came here and asked a question, which has been answered a few times over, we have variously tried to explain why the answers we have given are what they are, yet you just seem to be taking offence at the fact they aren't what you appear to want the answer to be.

What 'proper forum' are you referring to?
 
Really?? Obviously the Adiabetic returned a value a 0, that is why a NON supplymentary was not installed. Why are you so insistent on this? The equation is not hard hard to follow anyway?
 
Really?? Obviously the Adiabetic returned a value a 0, that is why a NON supplymentary was not installed. Why are you so insistent on this? The equation is not hard hard to follow anyway?

Could you possibly help those of us with inadequate knowledge out by helping us understand what you meant by a supplementary? It's not a term which appears in the regs other than supplementary bonding?

The adiabatic equation used in bs7671 cannot return a value of 0 for any real-world figures.
The reason for people being insistent on it is that it is the method of sizing a cpc which gives the most economical size.
 
Really?? Obviously the Adiabetic returned a value a 0, that is why a NON supplymentary was not installed. Why are you so insistent on this? The equation is not hard hard to follow anyway?


What do you mean by that's the reason a 'NON supplementary' was not installed as you put it? If you mean by running in a separate earthing conductor along side of the cable then obviously the designer has obtained the necessary information from the manufacturer and found the armour to be adequate....How ever your question wasn't that was it? Your question was about taking a fly lead from the banjo to the earthing terminal in the enclosure.
 

Reply to Earthing inside a submain panel from main swa incomer in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
605
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
2K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top