OK guys n girls, first take a look at the table posted below
https://www.dropbox.com/s/820yq4v3l2zj1m8/swa_armour.pdf?dl=0
You can clearly see that a thermoplastic swa (FP600) of 150mm does not require a supplymentary earth.
Now with this FP600 Terminated directly onto the panel, and not through a gland plate, to me this termination is sound, and can handle any fault current. The R1R2 of the cable is 0.01 ohms back to the supply, tested at the gland. This same value is obtained from the earthing terminal inside the panel.
Hope this makes things clear.
Really?? Obviously the Adiabetic returned a value a 0, that is why a NON supplymentary was not installed. Why are you so insistent on this? The equation is not hard hard to follow anyway?
Really?? Obviously the Adiabetic returned a value a 0, that is why a NON supplymentary was not installed. Why are you so insistent on this? The equation is not hard hard to follow anyway?