HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,277
Reaction score
5,772
Location
Gloucestershire
I am soon to install some weatherproof sockets and a commando socket in a field. This will be around 80m from an existing consumer unit in a barn. Earthing is PME.

The commando socket will be for a cooler. The weatherproof socket(s) will be to plug in heating mats and cables (for soil). These will be inside a polytunnel.

I was just wondering if there is any reason why I should not use the PME? Section 705 mentions not using PME in relation to livestock, but it doesn't relate this to horticultural premises. Just wondered what your thoughts were?

Cheers 🙂
 
There's several things to consider and the simple answer is to TT the external supplies.

Firstly, is any part of the installation in the field likely to be extraneous? Perhaps the chiller will have metal legs onto the soil or the heat mats may have exposed conductive parts in contact with the soil? If you use the TNCS you'd need a suitable bonding conductor back to the MET.

Secondly, the TNCS cpc may not have the same potential as true earth so there's a risk of tingles for those people stood in a wet field who touch the exposed conductive parts of the chiller etc.

Finally, in the unlikely event of a lost PEN conductor, the exposed conductive parts would have an increased potential vs the people standing on the soil.

If you go TT, you'd be likely to need a submain out to the field and then a small DB in some form of cabinet where you can devorce the TNCS earth and go TT. This would also give some flexibility for alterations or additions in the future.
 
There's several things to consider and the simple answer is to TT the external supplies.

Firstly, is any part of the installation in the field likely to be extraneous? Perhaps the chiller will have metal legs onto the soil or the heat mats may have exposed conductive parts in contact with the soil? If you use the TNCS you'd need a suitable bonding conductor back to the MET.

Secondly, the TNCS cpc may not have the same potential as true earth so there's a risk of tingles for those people stood in a wet field who touch the exposed conductive parts of the chiller etc.

Finally, in the unlikely event of a lost PEN conductor, the exposed conductive parts would have an increased potential vs the people standing on the soil.

If you go TT, you'd be likely to need a submain out to the field and then a small DB in some form of cabinet where you can devorce the TNCS earth and go TT. This would also give some flexibility for alterations or additions in the future.
Thanks for this post. I had thought of all of those points apart from the first one which is probably the most important as it's the most likely to occur! So thankyou 😀
The simple option does seem to be TT.

Just thinking further. If I TT it, then what happens to any extraneous conductive parts then? In a house if it is TT, we still have main bonding to extraneous. Would I still have to bond extraneous in this case? I think this is a silly question and the answer is 'yes', as under fault conditions there will be a potential between exposed conductive parts and extraneous? It's the fact it's in a field, it's throwing me a little. it's outside of my happy domestic comfort zone.
 
Firstly, is any part of the installation in the field likely to be extraneous? Perhaps the chiller will have metal legs onto the soil or the heat mats may have exposed conductive parts in contact with the soil? If you use the TNCS you'd need a suitable bonding conductor back to the MET.
Actually, just read GN8 and parts of the electrical installation aren't considered to be extraneous, so please ignore that paragraph. Everyday's a school day!
 
Actually, just read GN8 and parts of the electrical installation aren't considered to be extraneous, so please ignore that paragraph. Everyday's a school day!
Can you expand a little ImpededLoop? "parts of the electrical installation aren't considered to be extraneous"? What does 'part' mean? The coolers legs stuck in the ground?
ps.. where abouts in GN8 are you reading? I'll have a look.
pps.. I've had a look, I can't find it.
 
Last edited:
Part 2 of 7671 page 30.

Section 6.1 in GN8 (it's a 17th edition version though...)
Same as mine then 😄
I see, you are just talking about the definition of an Ext CP.
I think a cooler with metal legs in the ground would be be classed as extraneous and need bonding (assuming it tested <23K).
 
Last edited:
Metalwork of electrical appliances are exposed conductive parts and are earthed to the electrical installation they are not extraneous.
Thanks Westward.
edit.. even though I have time to edit my clearly wrong previous post, I shall leave it there to highlight my ignorance.
 

Reply to Earthing requirements for a field? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top