True it could be TNCS...
Unfortunately I won't be able to find out where the other end goes..
Ze reading is 0.19 Ohms, isn't very low as for tt system?
 
True it could be TNCS...
Unfortunately I won't be able to find out where the other end goes..
Ze reading is 0.19 Ohms, isn't very low as for tt system?
It's not likely to be TT at 0.19 Ohms (never seen that low a value). If the L-N impedance is higher than Ze then I'm voting with Karin and Spary for TNCS. Is there a prize for the correct answer ? :)
 
Well it's 0.16 Ohms.. What now?
A lollypop as a reward hehe
Is it true that if impedance between L-E is the same as between L-N then it's a TNCS?
 
There used to be a requirement to stake PME systems to keep the resistance to earth below 20 ohms maybe that is what it is?
 
If it is in a block then that earthing stud could well be doubling up as the Building Network Operators earth marshalling point and the conductor rising from the duct could be a main protective bond of the incoming water / gas / steel (although this does look potentially a bit undersized).
I would be contacting the DNO to ask what the earthing system is and what the size of the supply is so that you are able to confirm adequacy of the bonding in relation to the supply neutral
 
Thanks guys for all your help, much appreciated.
I phoned the ukpowernetworks (London area) and they said they don't have this information... something is not right.
I'll call them again on Tuesday.

Thanks again and enjoy your weekend!
 
It’s all covered in the UKPN online documentation if you care to look for it.

It’s glaringly obvious what the earthing arrangement is.
 

Reply to Earthing System in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
706
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top