Earthing systems with agricultural premises | on ElectriciansForums

Discuss Earthing systems with agricultural premises in the UK Electrical Forum area at ElectriciansForums.net

A

AJO

Hello all

I've just been recently asked to do some remedial work in a farm for insurance. The supply is 3 phase and the existing earthing system is TNC S and I am going to convert this to a TT system which is in a cattle shed. From the main consumer unit I intend to resupply a consumer unit in some adjacent outbuildings which also 3 phase. My questions are would I be correct in installing two separate earth rods? 1 at the mains end and 1 at the out build?? Run a separate earth with the swa to the out build if I was enable to put a stake in? Also 300mA incomer at the main consumer unit?

your help would be greatly appreciated
 
Depends on the out building, if it has other earth paths in the out building (water pipe, structural steel etc) then will need separating from the incoming earth and staking again.
 
Why would it need a seperate stake in that situation?

If you can get a good enough Ra at the intake then all is ok. It may be the case that a second earth electrode at the second building may be required to get the Ra down for the whole installation.
 
I wont try to expand and complicate things. As much as i don't like to quite the regs, you need to read the bit in Part 7 of the BGB about Agricultural and Horticultural premises. Earthing systems and what system you can and can't use in different parts of those locations are well explained. This may swing your proposal to some degree.

Cheers...........Howard
 
Every building you intend converting from TNC-S to a TT system should be rodded. In fact i'd prefer to see two linked rod positions for each building. There is absolutely no need to isolate the rod positions, in fact it is far better to link the TT'd building rods, it will greatly bring down the overall Ra value. And don't TT the main farm house, that is far better being left on the DNO's TNC-S earthing system...

As SB above suggests, in fact i'd go as far as saying it's imperative you make yourself familiar with the requirements for Agricultural and Horticultural premises. Providing certain criteria are met, TNC-S/PME can still be utilised in buildings housing farm animals...
 
TT the outbuilding but not the house. Why would you put a rod in at the house? That should not be TT'd. Run an SWA, no additional earth is required.

At the outbuilding end, isolate the armouring from the outbuilding DB. This is there to earth the sub main. Knock a stake in and connect an earth conductor from the stake to the MET at the new DB.
 
Sorry to jump in, Might be me been thick but do you meen remove bonding from gland / earth tag to sub bd, which I would do. But I was once told by a guy that you need to take swa gland out and put a piece of insulation under so no earth path present back to met, obviously put gland back in
 
Sorry to jump in, Might be me been thick but do you meen remove bonding from gland / earth tag to sub bd, which I would do. But I was once told by a guy that you need to take swa gland out and put a piece of insulation under so no earth path present back to met, obviously put gland back in

Yes correct as above
 
The earthing and bonding guidance note has some pretty clear explanations and pictures on the subject.

But basically any metal parts connected to the earthing system of the origin (armouring and gland) should be completely isolated from the sub board and in theory not enter the enclosure or be available to touch.
 
Sorry to jump in, Might be me been thick but do you meen remove bonding from gland / earth tag to sub bd, which I would do. But I was once told by a guy that you need to take swa gland out and put a piece of insulation under so no earth path present back to met, obviously put gland back in

You can get special SWA glands to isolate the armour, or you can nip off the exposed armouring and use a good quality stuffing gland at the isolated end of the SWA cable. Another point to make when talking about farm installations, is to always use brass locknuts/lockrings and tight fitting shrouds on SWA cables, or corrosion will become a real problem. ...What with all the chemicals now used on farms, and the legendary neglect associated with general farm installations!!!....
 
You can get special SWA glands to isolate the armour, or you can nip off the exposed armouring and use a good quality stuffing gland at the isolated end of the SWA cable. Another point to make when talking about farm installations, is to always use brass locknuts/lockrings and tight fitting shrouds on SWA cables, or corrosion will become a real problem. ...What with all the chemicals now used on farms, and the legendary neglect associated with general farm installations!!!....

surely it would be better to use adhesive shrouds.

ive done an install on a farm and the cleanest part was the septic tank lol

the problem you will have most of all is the farm hands most wouldn't think twice about fishing things out of septic tanks etc with bare hands or using plastic conduit to climb up etc
 
thanks for the replies guys.... the main supply is in the cattle shed where the distributor has provided a PME terminal, which isn't labelled, has existing equipments earth connected to it. I have read that TNC S supplies may be installed. would be best to use this for the main db, earth armourings,disconnect the armourings at sub main and try find somewhere to stake it that end?
 

Reply to Earthing systems with agricultural premises in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
702
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
Suggestions for best place to find suitable installers to quote?
Replies
4
Views
324

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top