Hello guys n gals,
Did n EICR other week in a flat where the shower circuit was 40A mcb with RCD protection, 6mm cable. Only about 10M run.
The 8.5kw shower had been replaced by the tenant for a 10.5kw one (old one was still in the cupboard is how I know).
Unusually, the installation supply voltage was 254V - Which I have entered in the report that the supplier should be informed about.
As this brings the present shower down to 41A it is presently operating without issues. However, if the supply voltage was to be bought down to a more suitable level in the future I could see issues arising so I coded it C2.
Just wondered if anyone had a different view?
Ta in reading & hope you're having a fun day