Why are you guys worried about whether another sparks would get a belt from it? From the point of view of the final user and not another sparks, The question is this, is it an immediate danger? No
is it a potential danger? No
Does it comply with regs? No
Therefore C3
You are reporting on the installations condition and whether the installation is safe for continued service in the fashion to which it was installed for. Neutrals and earths in the wrong terminal numbers does not make this unsafe.
Reply to EICR code thoughts please? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I would C2 this, cable is not suitable for the environment its installed in, we would C2 a socket for equipment likely to be used outside , cable...
The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...