I've been and done an inspection on a rented property today. Normally I am pretty sure of myself with codes but caught myself second guessing today so thought it might help freshen my head up to run a couple of points by the forum for opinion.
First one is a spur from a 2.5mm 32A ring final. It leaves the MCB in 2.5mm and feeds a single socket for a washing machine under a counter, then also an above counter SFCU for a kitchen extract fan. Seeing as this would not be likely to be subject to overload due to the socket being used for a dedicated purpose and the total load being limited to less than that of the cable CCC I was thinking a C3.
A similar issue with the boiler feed. It is protected by a 6A MCB but is only in 1mm cable. As the potential load is limited I'm thinking only a C3 for the cable not being the minimum 1.5mm required for power circuits.
Thanks for your thoughts.
First one is a spur from a 2.5mm 32A ring final. It leaves the MCB in 2.5mm and feeds a single socket for a washing machine under a counter, then also an above counter SFCU for a kitchen extract fan. Seeing as this would not be likely to be subject to overload due to the socket being used for a dedicated purpose and the total load being limited to less than that of the cable CCC I was thinking a C3.