Hi,

A friend of mine owns a small unit, i have the papers from when it was last tested 10 years ago and also 15 years ago, but a lot of its been pulled out since then.

Ill be honest, I do not generally do periodics on this type of building and would like a bit of guidance.

I know how to test the circuits etc, its not that, thats the issue, its more with the BS number and what other peoples thoughts are for the setup where the board is really.

Take a look at the photos and see what you think, its a courier business and they wash vans out the front and take extensions out, nothing is RCD protected, generally the condition looks ok having walked round it yesterday.

[ElectriciansForums.net] EICR On small industrial unit[ElectriciansForums.net] EICR On small industrial unit[ElectriciansForums.net] EICR On small industrial unit[ElectriciansForums.net] EICR On small industrial unit
[ElectriciansForums.net] EICR On small industrial unit[ElectriciansForums.net] EICR On small industrial unit[ElectriciansForums.net] EICR On small industrial unit[ElectriciansForums.net] EICR On small industrial unit
[ElectriciansForums.net] EICR On small industrial unit[ElectriciansForums.net] EICR On small industrial unit
 
Ok I always thought machinery, especially rotating (motors etc) should drop all three phases if one phase drops out (unless the machinery itself has this type of protection, eg. undervoltage trip).

This is to prevent harm to operators but mainly to protect the equipment itself. If this is so wrong how come 3-pole mcb's are interlinked?

Teach me people :)

The motor overload relay in the starter will handle that, the supply to the starter will be quite happy on fuses.
 
Well I did my time years ago at Kier Sheffield, mainly domestic (decent homes scheme house bashing), but also worked on fire alarms, door entry systems etc. We did some small to medium commercial stuff which is my experience of 3 phase.

Generally it was new build so no existing older installs seen. Judging by my MISTAKEN initial post in this thread you can see I haven't had any experience with Industrial installs. Anyway a few of my mentors on commercial jobs ('experienced' time served sparks) would always suggest 3 pole mcb's for safer isolation on 3 phase systems. Their words repeated by me. Never seen a switch fuse feed a final circuit directly, only to feed sub boards generally from a bus bar chamber.

As always in this game I'm still learning, I have no desire to do Industrial and only stick to light modern commercial and domestic. I guess due to larger in-rush currents and high kilowatt machinery mcb's aren't practical compared to BS 88 fuses (etc). Basically what Alanl said in #15.
 
Well I did my time years ago at Kier Sheffield, mainly domestic (decent homes scheme house bashing), but also worked on fire alarms, door entry systems etc. We did some small to medium commercial stuff which is my experience of 3 phase.

Generally it was new build so no existing older installs seen. Judging by my MISTAKEN initial post in this thread you can see I haven't had any experience with Industrial installs. Anyway a few of my mentors on commercial jobs ('experienced' time served sparks) would always suggest 3 pole mcb's for safer isolation on 3 phase systems. Their words repeated by me. Never seen a switch fuse feed a final circuit directly, only to feed sub boards generally from a bus bar chamber.

As always in this game I'm still learning, I have no desire to do Industrial and only stick to light modern commercial and domestic. I guess due to larger in-rush currents and high kilowatt machinery mcb's aren't practical compared to BS 88 fuses (etc). Basically what Alanl said in #15.
yeah we had to reconnect, test and comission a boiler house before.

because of the way the panels are we were getting readings too high for 60898 breakers so it went on test sheet as recommended swapping to bs88 (was the overloads causing it because of the dol starters)
 
yeah we had to reconnect, test and comission a boiler house before.

because of the way the panels are we were getting readings too high for 60898 breakers so it went on test sheet as recommended swapping to bs88 (was the overloads causing it because of the dol starters)

I'm getting lost again, here.....what and where did you test?
 
yeah we had to reconnect, test and comission a boiler house before.

because of the way the panels are we were getting readings too high for 60898 breakers so it went on test sheet as recommended swapping to bs88 (was the overloads causing it because of the dol starters)

Something smells a bit fishy here, how were the overloads having an impact on the supply MCBs ?
And why are you using 60898 (domestic) MCBs for a boiler house? Should they not be 60947s
 
Something smells a bit fishy here, how were the overloads having an impact on the supply MCBs ?
And why are you using 60898 (domestic) MCBs for a boiler house? Should they not be 60947s
the overloads were after the mcb's in the panel then out to the triacs then boilers i didnt check the breaker type i posted 60898's simply so you guys knew they were breakers
 
Something smells a bit fishy here, how were the overloads having an impact on the supply MCBs ?
And why are you using 60898 (domestic) MCBs for a boiler house? Should they not be 60947s
Why? How many 'd' type TP 60898 breakers, for example, have you seen in a house?
 
Why? How many 'd' type TP breakers have you seen in a house?

What on earth has that got to do with it? Any TP d type breaker you buy will be built to 60947, but will also, almost inherently, comply with 60898.
The point is that a breaker which complies with only 60898 is only intended for domestic use whereas a breaker built to both standards or just 60947 is suitable for all.
 
What on earth has that got to do with it? Any TP d type breaker you buy will be built to 60947, but will also, almost inherently, comply with 60898.
The point is that a breaker which complies with only 60898 is only intended for domestic use whereas a breaker built to both standards or just 60947 is suitable for all.

I would imagine that in a boiler house control panel they would have been built to spec. with 60898 labelled.
 
What on earth has that got to do with it? Any TP d type breaker you buy will be built to 60947, but will also, almost inherently, comply with 60898.
The point is that a breaker which complies with only 60898 is only intended for domestic use whereas a breaker built to both standards or just 60947 is suitable for all.

Is it always as clear cut as that Dave ? I have in front of me for example a 40A TP MCB, C curve, 10kA rated that states BS EN 60898 only. Would that have been produced with domestic application in mind ?

Not trying to be tetchy or argumentative mind, just expanding my knowledge
 
Is it always as clear cut as that Dave ? I have in front of me for example a 40A TP MCB, C curve, 10kA rated that states BS EN 60898 only. Would that have been produced with domestic application in mind ?

Not trying to be tetchy or argumentative mind, just expanding my knowledge
why does it need to comply if 10ka rating is satisfactory why do you need 15ka mcbs
 
Is it always as clear cut as that Dave ? I have in front of me for example a 40A TP MCB, C curve, 10kA rated that states BS EN 60898 only. Would that have been produced with domestic application in mind ?

Not trying to be tetchy or argumentative mind, just expanding my knowledge

BS EN 60898 'low voltage circuit breakers for use in household and similar applications'

BS EN 60947-2 'low voltage circuit breakers for use in industrial and similar installations'

So it all depends on how you define 'similar installations' , I think small commercial offices/shops would be, but what else?
 

Reply to EICR On small industrial unit in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Sockets will probably be ok on one, a little inconvenient in the event of a fault though, I'd probably like a 7th rcbo in. Wonder if hes linked...
Replies
93
Views
7K
suffolkspark
S
  • Question
Hello Dave, Thanks for taking the time to reply. I appreciate the info, I haven't updated this post yet, but I have since been talking to some...
Replies
3
Views
1K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top