Just a quick one.. I have been to a job today where the shower isolator switch had burnt out, as it wasn't RCD protected I replaced the switch with a 1 way consumer unit with an RCD.
My question is..do I need to do a full EIC or would a minor works do?
Cheers
Hi - the new "one way consumer unit which had an RCD" also had an MCB in it? This means (to me) there are now two circuits where there was one, each with its own earth loop and ADS times to be met.
Going with that analogy Wilko, if and I say if the OP had swapped the shower switch with a RCD / FSU instead of a small CU, would that not be similar, or the same as using a CU, after all, all he is doing is fusing down via the CB and adding a RCD? it's an imponderable I guess, which can/could argued either way, well that's how I tend to see it.
This is a EIC in my opinion. The supply to the shower isolator is now a distribution circuit.
Also the shower isolator did not burn out because there was no RCD installed.
You haven't wired a new circuit, you have altered an existing circuit MNW
Really bizzare..putting an RCD on a shower when there wasn't one there before..what was I thinking??
I agree, what were you thinking. Straight forward replacement switch with a departure on the Minor Works additional rcd protection not provided, existing circuit.
Reply to EICR or Minor Works??? in the UK Electrical Forum area at ElectriciansForums.net
For a new circuit or alteration the dead tests should be done first to ensure it is safe to energise.
Unless the circuit is new or has recently been tested/certified by a.n.other, I'm not sure how you prove the circuit is 'safe' to connect to...