dlt27

-
Joined
Jul 4, 2011
Messages
196
Reaction score
30
Hi all, I have done a few EICR's before however could do with a bit of advice on what codes you more experienced guys would give these observations;
1 Old 3036 DB made up of wooden base/back. (C3?)
2 Underszed main bond. (C3?)
3 Cooker switch mounted 18" above cooker (C3?)
4 Mutiple cct's in MCB (C3?)
Thanks for any input.
 
Any body has a wooden CU tell them they need a rewire, ask them if they can afford it and get out of there. Do not do anything last man in is responsible fail it on a visual charge them ÂŁ30 quid and get out of there.
 
I recently done a niceic solar course down south. The guy carrying out the course also carried out courses in eicr's. I put the question to him about what codes I should put to various observations ie ones that were safe but not up to current regs. (Ones I didn't think deserved a code). His reply was that anything that wasn't up to current regs. should be a code 3 because it would enhance the installation . I asked well why do away with the old code 4 then! I said I thought an eicr was carried out to see if an installation was in a safe condition not to see if it was up to current regs.
However he wouldn't have any of it...
 
Total and utter nonsense!
[ElectriciansForums.net] Eicr
Reckon he was waiting for a bite boss!
 
I recently done a niceic solar course down south. The guy carrying out the course also carried out courses in eicr's. I put the question to him about what codes I should put to various observations ie ones that were safe but not up to current regs. (Ones I didn't think deserved a code). His reply was that anything that wasn't up to current regs. should be a code 3 because it would enhance the installation . I asked well why do away with the old code 4 then! I said I thought an eicr was carried out to see if an installation was in a safe condition not to see if it was up to current regs.
However he wouldn't have any of it...

Well this is how we carry out EICRs. We use the C3 as a way of highlighting that everything is fine but these things could be improved.

Reading that leaflet from LSK though it says different. The jury is still out on this one for me.
 
There is no correct answer but you need to be confident with your own answers. Off the bat without seeing I would say:

1) C2 - wooden base DB coukd potentialy be dangerous.
2) C3 - as long as continuity is adequate.
3) C2 - potentially dangerous
4) C3 - as long as OCPD is rated appropriately to the conductor sizes.

got some regs to back those up fella????

1,2,4, no code. maybe a comment for 2 & 4.

3. C3.

IMO.edit: 2. code if <6mm.

need some more info on the multiple circuits in one breaker but other than that the above is pretty much how I see it too

Well this is how we carry out EICRs. We use the C3 as a way of highlighting that everything is fine but these things could be improved.

Reading that leaflet from LSK though it says different. The jury is still out on this one for me.

In what way?your opinion?, how things are done in your neck of the woods? Or it doesn't comply with the current edition and amendment of the regs but it doesn't have an impact on the installations electrical safety?


you should be able to back up all your observations with relevant regs,your not required to provide the reg numbers in your EICR (unless your client specifies so, which I would of thought some railway mobs would insist) if it's not dangerous, potentially dangerous or doesn't comply with the current regs then it shouldn't be on the report
 
got some regs to back those up fella????



need some more info on the multiple circuits in one breaker but other than that the above is pretty much how I see it too



In what way?your opinion?, how things are done in your neck of the woods? Or it doesn't comply with the current edition and amendment of the regs but it doesn't have an impact on the installations electrical safety?


you should be able to back up all your observations with relevant regs,your not required to provide the reg numbers in your EICR (unless your client specifies so, which I would of thought some railway mobs would insist) if it's not dangerous, potentially dangerous or doesn't comply with the current regs then it shouldn't be on the report

My regs don't fit in my back pocket, sorry.

I said 'off the bat' for a reason.

Can you back your opinion up with regs? I will try tomorrow.

No we do not put reg numbers in.

Just an opinion mate. No need to go all bonkers over it.

Oh no! I can't Adam & Eve it. I got rockin' horse all over me backed beans because of you now.
 
Hi all, I have done a few EICR's before however could do with a bit of advice on what codes you more experienced guys would give these observations;
1 Old 3036 DB made up of wooden base/back. (C3?) No code
2 Underszed main bond. (C3?) If it truly is undersized then yes, C3, I do however recommend a read of chapter 54 to verify this as I'm willing to bet it aint. If it aint, then no code
3 Cooker switch mounted 18" above cooker (C3?) No code
4 Mutiple cct's in MCB (C3?) No code
Thanks for any input.

There is no correct answer but you need to be confident with your own answers. Off the bat without seeing I would say:

1) C2 - wooden base DB coukd potentialy be dangerous. Wrong. No code
2) C3 - as long as continuity is adequate. As previously explained
3) C2 - potentially dangerous Wrong. No code
4) C3 - as long as OCPD is rated appropriately to the conductor sizes. Wrong. No code

My contribution in red

Never before have I seen such a well executed example of the blind leading the blind!
 
True. I'm getting a bit sick and bored with this lot.

What's worse than being sick and bored of threads like these???

Being sick and bored of life in general, then coming on here and finding threads like these!

Makes the thought of putting a shotgun in my mouth and pulling the trigger quite a pleasant distraction.
 
What's worse than being sick and bored of threads like these???

Being sick and bored of life in general, then coming on here and finding threads like these!

Makes the thought of putting a shotgun in my mouth and pulling the trigger quite a pleasant distraction.

Distraction, to be sure. At least Erwin was forced to take the pills....or so they reckon!
 
What's worse than being sick and bored of threads like these???

Being sick and bored of life in general, then coming on here and finding threads like these!

Makes the thought of putting a shotgun in my mouth and pulling the trigger quite a pleasant distraction.

WTF! Crap threads crap sparks crap whatever that's a terrible statement
 

Reply to Eicr in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
437
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top