View the thread, titled "Electrical Myth busting!" which is posted in Australia on Electricians Forums.

P

pencilpusher

First of all, Happy New Year to everyone...................

Now, having had a thread attract a scaremongerer this week about the "myth" of extending a PME suppy to an outbuilding, I am very interested to hear about electrical myths others have heard of and would like to share. (This is a serious thread to collate myths about electrical can and cannot do's - no other myths are welcome!) Maybe we could compile a list of the top ten electrical myths at the end.

I will start then - You cannot export (extend) a TNCS supply to an outbuilding ..........or else!

Over to you.......................:)
 
Last edited by a moderator:
What does this mean?

VIR ( rubberinsulated) cable . might be perished at ends, where the air has got to it. doesn't mean the whole cable is shot.
 
DNO will come out and remove their fuse at 9.00am and return to replace within 15 minutes of your phone call.
 

Reply to the thread, titled "Electrical Myth busting!" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top