Hi i mostly do commercial so not 100% up todate on the regs.

My mate wants me to wire up a ensuite for him. There is no bath or shower so im under the impression there are limited restrictions as there are no zones.

I am putting in two fused spurs and a down light.

Aslong as the spurs are rcd protected is this ok to do?

Cheers
 
is it just a bog and basin then? if so, it's not a special location, therefore RCD protection is only required for sockets and cables buried in walls ( 522.6.101 ).
 