Regulation 722.411.4.1 unequivocally and unambiguously states that: "a PME earthing facility shall not be used as the means of earthing for the protective conductor contact of a charging point located outdoors
OR that might reasonably be expected to be used to charge a vehicle located outdoors ..... ". Ergo it is self-evident that the
EV charger which has been installed adjacent to the entrance of the OP's garage could be reasonably expected to be used to charge a vehicle located outdoors. All the OP need do to create this very scenario would be to park his/her car outwith the garage then connect the charging lead between his/her car and the charging point.
Quod erat demonstrandum.
The OP stated in a previous post that he/she contacted the installer who advised him/her:
If you wish to use your charger to charge the car outside then regulations state the use of a TT earth is required, if the charge point is to be used inside then connection to your house earth is recommended
Whether or not the OP has any intention of charging his/her car outdoors is irrelevant. No provision has been made in regulation 722.411.4.1 for consideration of customers' wishes. What is of relevance, however, is that the regulation has not been complied with and has been breached by virtue of the fact that the installer has installed the charging point in a location where the point might reasonably be expected to be used to charge a vehicle parked outdoors.
Quod erat demonstrandum.
The installer should have been aware of the inherent risks involved and acted accordingly by connecting an earth rod to the charging point therefore making this dedicated circuit a TT arrangement. The crucial point that I am making here is that locating an EV charging point indoors does not negate the need for an earth rod to be connected to the charger. That a charging point installed indoors can be used to charge a vehicle located outdoors necessitates a TT arrangement.
Subject to conditions (i), (ii) and (iii) of regulation 722.411.4.1 being satisfied, connection of an earth rod to a T-N-CS arrangement is permitted. However, we can immediately eliminate two of these conditions as plausible options. Since the OP's charging point is connected to a single-phase supply, condition (i) does not apply here. Given that it would be next to impossible to achieve the ultra-low Ra value that would be required to ensure that an open-circuit fault in the PEN conductor supplying the installation does not exceed 70 volts rms, condition (ii) is a non-starter. But condition (iii) can be satisfied by installing a charger that does not require connection to an earth rod. The
Pod Point Solo is one such charger.
While regulation 722.413.1.2 permits the use of a fixed isolating transformer that complies to BS EN 61558-2-4 as a means of providing electrical separation for one electric vehicle supplied from one unearthed source, Mr. Smith and Mrs. Jones are not going to incurr an additional cost of several hundreds of pounds for an isolating transformer to be installed in their meter cupboard, assuming they had the physical space to accommodate the bulky transformer there in the first place.
So ultimately there were but two realistic choices open to whoever installed the OP's charging point: either install a charger that does not require connection to an earth rod, or install at least one earth rod to the charging point so forming a TT earthing arrangement for that dedicated circuit. Since the charging point that was installed in the OP's garage was not a model that would comply with the requirements of 722.411.4.1 condition (iii), the installer by default should have installed an earth rod and made the the earthing arrangement for that dedicated circuit TT.
Quod erat demonstrandum.

John Ward has produced an excellent and most informative video regarding the earthing arrangements for electric vehicle charging equipment. The segment between 10:25 and 11:09 explains the TT arrangements for a dedicated EV charging circuit. What JW says here is what I have been saying throughout this thread. So if I am wrong, then so too is JW. Is there anyone here who would like to step up to the plate and call him out along with the author of two articles that were published in
Connections in June 2018 and in
Professional Electrician in November 2018?
The installer of the OP's charging point also advised him/her:
Looking back at the information you provided, you requested that the charge point be installed inside the garage and we have assumed that this would be for the purpose of charging inside, we will look to clarify this to all customers going forward.
The assumptions of the installer are inconsequential. The requirements of regulation 722.411.4.1 are unequivocal, unambiguous, and perfectly clear. Crystal is opaque by comparison. A PME earthing facility shall not be used as the means of earthing for the protective conductor contact of a charging point located outdoors
OR that might reasonably be expected to be used to charge a vehicle located outdoors unless any one of the three conditions attached to that regulation can be satisfied.
The photographs below are of an install that I recently completed in the garage of a local car-hire company. The earthing system is T-N-CS. There was no need for any earth rods to be installed in this installation as all three charging points are located indoors and are located in such a manner that they could not ever be used to charge an electric vehicle located outdoors. If there had been even the slightest possibility of the client ever using any one of these chargers for outdoor charging, then rest assured that I would have connected each charger to an earth rod and undertaken a risk-assessment in accordance with section 6.8 of the Code of Practice for Electric Vehicle Charging Equipment Installation and attached a written risk-assessment document to the Electrical Installation Certificate.
The company who installed the OP's charger come across as being reasonable and approachable, The photos that the OP posted of the install indicate that it has generally been carried-out to a high standard. My advice to the OP, for what it;s worth, would be to ask the company to come back and carry-out a risk assessment with a view to converting the dedicated circuit for the charging point to a TT arrangement.
An alternative solution would be for the charging point to be replaced with a
Pod Point Solo. However, given that the install was part-funded by grants from OLEV and the Energy Savings Trust, there would almost certainly be complications. But as things stand, the charging point in its present state cannot be left as it is because it does not comply.
I wish the OP well and trust that a satisfactory outcome will ensue. Please keep us posted of developments.
And on that note, I shall now exit stage left. I've stated my case and will make no further contribution to this thread.