The non stat document that is applicable to the construction and use of test equipment is?
a- bs7671
b- gn3
c - gs 38
d - osg
When a number of additional circuits are connected to a distribtion board the overall resistance will?
a- Decrease
b- remain unchanged
c- be a average of circuit value
d- increase
This question is usually for insulation resistance and not resistance. Reckon its a typo :86:
Which one of the following devices is suitable for PFC in excess of 60kA?
a-bs 88-2
b-bs 3036
c- bs 1362
d- bs en 60898
Where no supply is availble, a test of earth electrode resistance for a installation forming part of a TT system can be carried out using?
a-Earh fault loop impedance tester
b-a continuity tester
c- An earth electrode teste
d- a low resistance ohm metre
Think about it Peter, to use an EFLI tester you need a supply voltage, the question is telling you this isn't available::
The earth fault loop impedance of a radial circuit must be measured at?
a-the origin of the circuit
b-any convenient part of the circuit
c-the furthest part of the circuit
d-every switch on the circuit
Its asking to measure EFLI for the radial circuit, not the supply so its wrong ::
><
Why? Do you think they are correct?
the last one was.
My try
here we go
The non stat document that is applicable to the construction and use of test equipment is?
a- bs7671
b- gn3
c - gs 38
d - osg
When a number of additional circuits are connected to a distribtion board the overall resistance will?
a- Decrease
b- remain unchanged
c- be a average of circuit value
d- increase
Which one of the following devices is suitable for PFC in excess of 60kA?
a-bs 88-2
b-bs 3036
c- bs 1362
d- bs en 60898
Where no supply is availble, a test of earth electrode resistance for a installation forming part of a TT system can be carried out using?
a-Earh fault loop impedance teste
b-a continuity tester
c- An earth electrode teste
d- a low resistance ohm metre
The earth fault loop impedance of a radial circuit must be measured at?
a-the origin of the circuit
b-any convenient part of the circuit
c-the furthest part of the circuit
d-every switch on the circuit
You don't take a Zs at just the origin or just the last point on a circuit.
Which, will be the furthest part of the circuit.