Hi all just done this **** exam and these are the questions a rememberd and wrote down in notes,,
Last edited by a moderator:
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Exam question help in the UK Electrical Forum area at ElectriciansForums.net
honestly mate my heads in bits the gola in split into i think6 sections and u need 56%+ in each
i got 100% - 100% - 89%-90% 55% and 88% and bloody failed cuz the 55%
another question i got was
A test that is automatiacally conducted when carrying out a test on a ring final circuit continuity is
a- insulation resistance
b- polarity
c- RCD operating times
d- loop impedance
highlighted my answer, that right?
Bugger my damn mind two are live only tests and the other is a seperate test to what you are carrying out.
Q1-GS 38
Q2-Decrease
Q3-BS 88-2
Q4- An earth electrode tester
Q5- The furthest part of a circuit (its mentioning the radial circuit, and it does not say lighting circuit is there, so where is them switches come from in answer D).
Here is the copy of paragraph in Practical guide to inspection and testing.
Measurethe resistance of earth fault loop impedance at the furthest point of
thecircuit using the correct instrument ( rememberthe furthest point is the end of the
circuit, not necessarily the furthest distance from thedistribution board ). Record the
valueobtained onto the test result schedule.
Q1-GS 38
Q2-Decrease
Q3-BS 88-2
Q4- An earth electrode tester
Q5- The furthest part of a circuit (its mentioning the radial circuit, and it does not say lighting circuit is there, so where is them switches come from in answer D).
Here is the copy of paragraph in Practical guide to inspection and testing.
Measurethe resistance of earth fault loop impedance at the furthest point of
thecircuit using the correct instrument ( rememberthe furthest point is the end of the
circuit, not necessarily the furthest distance from thedistribution board ). Record the
valueobtained onto the test result schedule.
was looping in the book and its says you can use them 2 testers to complete a earth electrode test so as efli needs a supply then has to be the other >
Every point on a circuit. So every socket, every light switch every light fitting etc
Check post 34 mate, its telling you exactly which one it was.
Got it in one!ye i think earth electrode tester ye?
what about this one?
In order to ensure that the risk of electric shock under fault conditions is significantly reduced, it is important that?
a- Basic protection is provided
b - All protective conductor terminations have a warning notice
c- All protective conductors are in place and disconnection times are met
d- The earthing conductor must not be less than 25mm squared
my answer highlighted
depends....has the circuit had an (R1 R2) carried out at each point served?....if so then Zs at furthest point...5 is also