Evening all could anyone please tell me the the maximum ze for tt systems the jobs entail Rec cut out fuse bs88 16a to feed 1x 30 ma rcd fuse spur for feeding socket outlet what should the max ze be please
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss External earth fault loop tt system in the UK Electrical Forum area at ElectriciansForums.net
Good point, I hadn't thought that far ahead. Was just having a rant. I don't think we did distribution transformers on my 5 week course, although that may have been in the two weeks I was off having it large in Ibiza. Can't have missed that much.
On a serious note, the DNO is responible for getting current to and from the installation (Line and Neutral) so why shouldn't they also be responsible for the fault current path as well?
Having worked for one of the RECs and got involved with supply and distribution the pme system is the preffered system used at all times by them , you will probably notice more and more overhead TT systems being converted with the new aerial buched conductor(ABC) network , you will also probably have noticed that every 4th pole as required by Distribution Supply regs that the neutral is bonded down to earth with a stake , this is for safety reasons in case the neutral breaks down , There are drawbacks of course firstly the need to test for polarity on the incomming supply and also the loss of the neutral on the incoming supply , and the consequences. But there is no difference whether there are 10 or 100 properties being supplied , as long as the Ze is below the 0.35 . The fault current that returns back to the transformer is no longer fault current from the cut out back to the Tx , only within the customers premises , Yes it is correct that the REC would need to be contacted if you want a PME conversion , you can not do it yourself , but as time goes by more and more of the old TT systems will be converted , Indeed many olde
Nope, i doubt that very much!!
Wind up merchant, nothing more, nothing less!! lol!!
TN-S systems mostly remain TN-S systems , what we are talking about here is a TT system!!
The older TT systems that are converted are allways assesed and Ze readings taken into account before conversion . Their are exceptions where even with a PME supply you would have to install your own earthing system of course!!
Are you accusing me of lying?...:toetap05:
Maybe i wouldn't go as far as that!! But a wind up merchant, you most definitly are!! lol!!
Of course not, you've freely admitted that you've never even tried to achieve better, and that was the basis of this thread!! All too easy to fall in to compromise mode, and rely on a single RCD ....Well while it's working correctly that is!! ..lol!!
Go and ask your Engineer if that is always correct or not!! You may be very surprised by the sound of it!! lol!! Think you must have been working on relatively all new PME installations, and not on existing converted cables that are in excess 60+ years old!! Most of the older TN-S cables that are now beginning to breakdown haven't been completely converted either, many being over the 0.35 ohm, and also carrying TN-S earthing on sections of the same cable!!
I can think of a few valid reasons for the DNO to refuse connection to a PME converted supply, as well as too converted overhead systems as well!!