Evening all could anyone please tell me the the maximum ze for tt systems the jobs entail Rec cut out fuse bs88 16a to feed 1x 30 ma rcd fuse spur for feeding socket outlet what should the max ze be please
 
Max 1667 ohms is so no more than 50 volts can appear on earthed metalwork.
Anything above 200 ohms is classed as unstable and likely to increase in frozen or dry soil conditions.

As has been said, fine while the RCD is functioning!!! lol!! You'd need to go down a lot more than that for a stable system, ...believe me!! Your ground/soil conditions would be absolute crud, to go down any depth and end up with just 200 ohms!! lol!!
 