Hi all. Had a phone call about a tripping RCD. The customer had narrowed it down to the kitchen ring. When I go there,it was indeed the kitchen ring causing the tripping. Firstly checked the usual,nothing plugged in to any of the sockets. Checked the connections at the sockets,these were all fine. Checked end to ends,had continuity on L,N & E. Carried out IR between LN & E at 250v,very low reading,virtually zero. Also tested L-E N-E & L-N. All very low. Now,the cables in the kitchen are red/black and the cables at the board are Brown/Blue. There no sign of any crimps etc at the board (which by the way is a total mess). So I’m thinking hidden joints/jb could be the source of the problem?? Any pointers would be appreciated!
 
Nah, it'll be an existing socket(s) from the previous kitchen install, buried under some tiles/plaster somewhere. If fault finding, gonna take longer than running in some new cables, I'd be tempted to do that.
 
None that I can see and the customer reckons there’s just the 3 sockets in the kitchen itself. No visible fcu’s etc.
Hi - yes been told this by Customer a few times :rolleyes: . Perhaps safely isolate and test L-N, first IR (250V). If IR is big, then ok - no loads still connected. If small, do continuity and if this is not o/c you should keep looking. Domestic loads typically range from about 20 Ohms to 20k Ohms. Some little device may still be connected and be faulty. Not saying its not a cabling fault, just another idea :) .
 
Hi - yes been told this by Customer a few times :rolleyes: . Perhaps safely isolate and test L-N, first IR (250V). If IR is big, then ok - no loads still connected. If small, do continuity and if this is not o/c you should keep looking. Domestic loads typically range from about 20 Ohms to 20k Ohms. Some little device may still be connected and be faulty. Not saying its not a cabling fault, just another idea :) .
I’ve IR tested at 250v,readings come back at virtually zero. Not even high enough to suggest anything still connected.
 
I’ve IR tested at 250v,readings come back at virtually zero. Not even high enough to suggest anything still connected.
Hi - Many IR testers fall in a heap when presented with a low impedance and tell you it's zero. My continuity tester will happily tell me 150 Ohms when there's a lamp still in circuit. But try that with the IR and it's zero. If I did IR only I'm chasing a cabling fault ... continuity result tells me there's likely a load still connected.
 
Hi - Many IR testers fall in a heap when presented with a low impedance and tell you it's zero. My continuity tester will happily tell me 150 Ohms when there's a lamp still in circuit. But try that with the IR and it's zero. If I did IR only I'm chasing a cabling fault ... continuity result tells me there's likely a load still connected.
The problem is,I’m getting some horror stories of diy Dave striking at this house. There’s a very good chance that there’s possibly more sockets hidden behind kitchen units etc. Some of the things that the owner told me about when they bought it the place...... I’ll double check that there isn’t an outside light or something. Apart from that,it would mean ripping the kitchen to bits!!
 
Hi - Many IR testers fall in a heap when presented with a low impedance and tell you it's zero. My continuity tester will happily tell me 150 Ohms when there's a lamp still in circuit. But try that with the IR and it's zero. If I did IR only I'm chasing a cabling fault ... continuity result tells me there's likely a load still connected.
Normally my fluke will give a reading that indicates a load still connected. It will slowly start to rise then stop.
 
New ring going in next week. I’ll try get a picture of the board while I’ve got the lid off..... I’d love to hear from some of the older guys to see if it’s one of the worst they’ve seen!!
 
New ring going in next week. I’ll try get a picture of the board while I’ve got the lid off..... I’d love to hear from some of the older guys to see if it’s one of the worst they’ve seen!!
Look forward to it.
 
You test each leg at every socket. If there’s a hidden jb or socket behind a cupboard and it tests ok just leave it. Not ideal, but they might change the kitchen again before a problem arises.
Think rewiring the whole rfc is a bit much when it could be just one bad connection somewhere.
 

Reply to Fault on kitchen ring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
349
Very technical :D
    • Like
Replies
9
Views
424

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top