Hi All

Taking a Zs from a light switch and am reading 160 volts between L & E.
What would you code this. I think it could be a neutral fault but I don't have the time available to investigate. The location is a hotel room.
Out of curiosity why are you quoting the units of zs in volts??
I thought it is measured in ohm
 
That's lovely, but as far as I know completly irrelevant to your original question and any testing carried out to bs7671.
This suggests you have less than a years experience of working on installations at lv and to bs7671, so approximately the same experience as a first/second year apprentice.

I agree with your 1 year experience wrt the UK. I think you should take into consideration my 40 years experience on projects in the mining industry in southern and East Africa, working to the mining regs
I served my apprenticeship(5 years)in the UK. The bit about 11kV etc was me having a hissy fit. (Western10) thought it funny.Sorted out the fault today. I was looking for coding. In South Africa the mines set their own more stringent regs i.e lack of labelling is a C1. So I just wanted to know what the forum thought
Do enlighten us, what is the joke?
You are carrying out an eicr, what is the joke?
Electrical safety at any voltage is far from a joke, if you have a clue you will realise electricity can, and will, kill without any regard for your opinion of whether it is funny or not.

Personally I don't care, but I'm lead to believe that the death of humans is unacceptable?

However I am curious as to how a liver and bacon casserole would taste with hunan liver? I've made it with all of the commonly available livers but humans are somewhat harder to come by for some reason? Perhaps once a few people have died from your approach to electrical safety you could cut out their livers and send them to me, I'll be happy to invite you to dinner to try this particular delicacy.
 
However I am curious as to how a liver and bacon casserole would taste with hunan liver? I've made it with all of the commonly available livers but humans are somewhat harder to come by for some reason? Perhaps once a few people have died from your approach to electrical safety you could cut out their livers and send them to me, I'll be happy to invite you to dinner to try this particular delicacy.

I think admin need to change your screen name to Hannibal Lector lol
 
I agree with your 1 year experience wrt the UK. I think you should take into consideration my 40 years experience on projects in the mining industry in southern and East Africa, working to the mining regs
I served my apprenticeship(5 years)in the UK. The bit about 11kV etc was me having a hissy fit. (Western10) thought it funny.Sorted out the fault today. I was looking for coding. In South Africa the mines set their own more stringent regs i.e lack of labelling is a C1. So I just wanted to know what the forum thought

Ok. Out if inteest, Where did you find the broken / disconnected cpc then?
 
Do enlighten us, what is the joke?
You are carrying out an eicr, what is the joke?
Electrical safety at any voltage is far from a joke, if you have a clue you will realise electricity can, and will, kill without any regard for your opinion of whether it is funny or not.

Personally I don't care, but I'm lead to believe that the death of humans is unacceptable?

However I am curious as to how a liver and bacon casserole would taste with hunan liver? I've made it with all of the commonly available livers but humans are somewhat harder to come by for some reason? Perhaps once a few people have died from your approach to electrical safety you could cut out their livers and send them to me, I'll be happy to invite you to dinner to try this particular delicacy.
I take safety very seriously the nature of my previous work dictates that. The joke was me having a hissy fit wrt 11kV not the fault.
I 'm sorry I brought out the Hanibal Lector in you(that is a joke)
 
I agree with your 1 year experience wrt the UK. I think you should take into consideration my 40 years experience on projects in the mining industry in southern and East Africa, working to the mining regs
I served my apprenticeship(5 years)in the UK. The bit about 11kV etc was me having a hissy fit. (Western10) thought it funny.Sorted out the fault today. I was looking for coding. In South Africa the mines set their own more stringent regs i.e lack of labelling is a C1. So I just wanted to know what the forum thought
Dont get mixed up with mines regs ,they are completely different from BS7671.
Forget about them and get up to speed with 18th Edition
 

Reply to Fault on lighting cct prevents taking Zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
460
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
949
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
895

Similar threads

Any electronics in circuit that might be skewing the readings? Smokies. Or smart switches? Might have been covered already, but what about...
2
Replies
25
Views
716
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
493

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top