Fault on lighting cct prevents taking Zs | Page 4 | on ElectriciansForums
Discuss Fault on lighting cct prevents taking Zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Then join E & N together , Metrel testers have a double end on one of the probes to do this. Apart from this the OSG shows how to take Zs from a light sw.
Yeah have done that before and you would expect readings to be the same but they weren't.
Does seem more accurate with the N connected, but maybe that's just the meter I was using at the time, when compared with a mates MTF 1552 which had been recently calibrated.
In these days of multifunction testers the idea of getting 2 identical test results from 2 seperate tests are long gone. That's the big disadvantage with MFT's
Reply to Fault on lighting cct prevents taking Zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Any electronics in circuit that might be skewing the readings? Smokies. Or smart switches? Might have been covered already, but what about...
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...