Grant McLaren

I am puzzling over an intermittent fault on a ground floor/kitchen socket circuit. Initially it seemed as soon as the oven switched on the RCD would trip. However, after unplugging the oven, I used a socket tester on other sockets, which would sometimes trip the RCD. It's pretty random, sometimes it will trip as soon as you plug something in, other times not. Zs reading were fine. The ring main has been broken, although the earths are still continuous. From what I saw, the socket circuit has not been done well.

When I left the property yesterday everything was on, but I'm waiting for a call from tenant to say it's tripped again.

Any thoughts on what it could be and why it has suddenly started now?

Regards.
 
You say you have continuity beteeen E-N, that may not trip if the current still finds a return path on the neutral which wouldn’t trip the RCD
I didn't know that ring mains weren't used anymore, although I independently stopped using rings ages ago. Whenever, I encounter an old ring, I assume it is broken and downgrade to 20amp.

Why do you assume that? Testing the circuit correctly will verify wether it’s good for continued use, not guess work on your part.
 
Wha tests did you carry out and what were the results from then tests?
Zs 0.9ohm was about this highest reading.
tested continuity between line, neutral and earth, I guess this is a form of IR test.
And opened up most of the sockets for a visual inspection. Apart from a few loosely tightened terminals, which are now tight, all seems fine.
RCD is working as it should.
Didn't do a R1+R2 test (although I should have), but let's assume there is something wrong here, why would it only now start presenting problems, when nothing in the installation has changed.

One final thing, I'm anticipating returning the property to get this sorted, but I thought first I'd get some thoughts from some friendly sparks. At least I found some sparks.
 
I didn't know that ring mains weren't used anymore, although I independently stopped using rings ages ago. Whenever, I encounter an old ring, I assume it is broken and downgrade to 20amp.

He doesn't mean the ring form isn't used any more. He means the terminology for a domestic ring circuit is 'RFC' and has been for some time.

Surely you don't just downgrade every ring circuit you come across as a matter of course??
 
Whenever, I encounter an old ring, I assume it is broken and downgrade to 20amp.

I really, really hope that you are being sarcastic with this comment....
 
He doesn't mean the ring form isn't used any more. He means the terminology for a domestic ring circuit is 'RFC' and has been for some time.

Surely you don't just downgrade every ring circuit you come across as a matter of course??
If I do work on it I do, with the possible exception of a kitchen or utilities circuit, since they might need the extra juice. NICEIC assessor thought it was a good idea. Besides, I thought the UK was moving away from rings, since they were originally used for old school heating systems.
 
I do know what ring final circuit is, I just haven't heard it referred to as RFC.

I didn't know that ring mains weren't used anymore, although I independently stopped using rings ages ago. Whenever, I encounter an old ring, I assume it is broken and downgrade to 20amp.
Why?
 
If I do work on it I do, with the possible exception of a kitchen or utilities circuit, since they might need the extra juice. NICEIC assessor thought it was a good idea. Besides, I thought the UK was moving away from rings, since they were originally used for old school heating systems.

Each to their own.
Not originally for heating systems no - just for general domestic use. Copper shortages and all that.
 

Reply to Fault on socket circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
693
  • Question
I misread it.
    • Like
Replies
13
Views
941

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top