G

Grant McLaren

I am puzzling over an intermittent fault on a ground floor/kitchen socket circuit. Initially it seemed as soon as the oven switched on the RCD would trip. However, after unplugging the oven, I used a socket tester on other sockets, which would sometimes trip the RCD. It's pretty random, sometimes it will trip as soon as you plug something in, other times not. Zs reading were fine. The ring main has been broken, although the earths are still continuous. From what I saw, the socket circuit has not been done well.

When I left the property yesterday everything was on, but I'm waiting for a call from tenant to say it's tripped again.

Any thoughts on what it could be and why it has suddenly started now?

Regards.
 
How many circuits are controlled by that RCD. If it trips randomly it could be that the total leakage to earth is more than 30mA, that would explain why it trips when plugging into different sockets etc.
I had exactly the same happening on a few occasions in domestic installations.
 
^^ I did say this in a roundabout way in post #2

But I suspect the op doesn’t understand the benefits of these meters .......

[ElectriciansForums.net] Fault on socket circuit
 
If the ring is broken then the chances are at least one of the live wires has come out of its terminal and is loose behind an accessory; every time this touches against anything which is earthed (including a metal backbox) the rcd will trip.
Changing the protective device won't stop this.

... Or have I missed an 'inside joke'?
 
I brought this up last week about idiotic random pics that keep being put up, tedious, irritating and boring.
I feel the same way about most of Pete's posts - I don't need a dedicated post to tell me he agrees with someone when there's a special button for precisely that purpose, or that he has "nil experience" in the matter in hand but going to have a guess anyway.
Do your worst, I've got a galvanised bin lid.
You got any of that popcorn left Strima?
 

Reply to Fault on socket circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
357
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
322
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
369

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
655
  • Question
I misread it.
    • Like
Replies
13
Views
905

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top