G

Grant McLaren

I am puzzling over an intermittent fault on a ground floor/kitchen socket circuit. Initially it seemed as soon as the oven switched on the RCD would trip. However, after unplugging the oven, I used a socket tester on other sockets, which would sometimes trip the RCD. It's pretty random, sometimes it will trip as soon as you plug something in, other times not. Zs reading were fine. The ring main has been broken, although the earths are still continuous. From what I saw, the socket circuit has not been done well.

When I left the property yesterday everything was on, but I'm waiting for a call from tenant to say it's tripped again.

Any thoughts on what it could be and why it has suddenly started now?

Regards.
 
You say you have continuity beteeen E-N, that may not trip if the current still finds a return path on the neutral which wouldn’t trip the RCD


Why do you assume that? Testing the circuit correctly will verify wether it’s good for continued use, not guess work on your part.
Electricians don't guess only plumbers
 
You say you have continuity beteeen E-N, that may not trip if the current still finds a return path on the neutral which wouldn’t trip the RCD


Why do you assume that? Testing the circuit correctly will verify wether it’s good for continued use, not guess work on your part.
Electricians don't guess only plumbers
 
english barry

[ElectriciansForums.net] Fault on socket circuit
 
So if you do a RFC and the readings are acceptable, do you assume the ring is not broken and that someone hasn't spurred off the ring?
I do know what ring final circuit is, I just haven't heard it referred to as RFC.

I didn't know that ring mains weren't used anymore, although I independently stopped using rings ages ago. Whenever, I encounter an old ring, I assume it is broken and downgrade to 20amp.
Wouldn't Ring Final Circuit, given you an itsy bitsy teeny weeny clue as to what RFC meant?
 
Gareth,
What was your ring continuity readings? What were your L-E & N-E insulation resistance test results you have given no indication that any proper fault finding has been carried out all you say is that the earth is continuous? And I still don't understand why you would go into a clients house and just change the protective device to 20A for an RFC just because it COULD have a spur off a spur or not have continuity without any testing'well that's the impression you have given me. Be upfront and give us some facts and you may get some very good advice from members drawing on their own past experiences. From what you have told us so far it may be a cable that has been drilled screwed.
 
Sooooo, based on the op’s original post and subsequent assumptions and answers a ring final circuit is BROKEN because it has a spur or spurs on it and yet he doesn’t test at every socket to confirm any spurs etc.....
 
Sooooo, based on the op’s original post and subsequent assumptions and answers a ring final circuit is BROKEN because it has a spur or spurs on it and yet he doesn’t test at every socket to confirm any spurs etc.....
No proper facts or test readings other than things being unplugged. I am sure that members would be more than willing to give possible causes if the OP has drawn a blank but basic testing needs to be carried out first.
 
Sooooo, based on the op’s original post and subsequent assumptions and answers a ring final circuit is BROKEN because it has a spur or spurs on it and yet he doesn’t test at every socket to confirm any spurs etc.....
That's about it Fitzy
 

Reply to Fault on socket circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
698
  • Question
I misread it.
    • Like
Replies
13
Views
946

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top