The Feeder Pillars I have worked on, relied on the sheath, be it SWA or some other armouring (not sure it was a long time ago) as the main earth conductor, you would need to look at SWA data to find out the CSA of the armour and then decide, if it's large enough in CSA to act as a Main Earth and a Bonding conductor, Atatched table is all the info I have, may help.
Thanks
 
Is the water pipe metal or plastic.
Hi.The water pipe comes out of the ground in plasic then changes to copper after the stopcock then about 2 foot later terminates in a garden type tap...all inside the enclosure.
I suppose what I'm trying to figure out is if it is an extraneous conductive part..(dont think so.)is it exposed conductive part (doubt it)so then it doesnt require equipotential bonding..If it was copper coming out of the ground it would be different.(I don't know now if it even needs the 6mm)
The other item is the cabinet itself I suppose it could become live under fault conditions but should it need an additional bond in addition to the CPC?? I cant think why it would.
Thanks for your thoughts
 
Hi.The water pipe comes out of the ground in plasic then changes to copper after the stopcock then about 2 foot later terminates in a garden type tap...all inside the enclosure.
I suppose what I'm trying to figure out is if it is an extraneous conductive part..(dont think so.)is it exposed conductive part (doubt it)so then it doesnt require equipotential bonding..If it was copper coming out of the ground it would be different.(I don't know now if it even needs the 6mm)
The other item is the cabinet itself I suppose it could become live under fault conditions but should it need an additional bond in addition to the CPC?? I cant think why it would.
Thanks for your thoughts
you should never rely on using the armoured wiring has a CPC.
specially 3 phase .
 
you should never rely on using the armoured wiring has a CPC.
specially 3 phase .
More often than not CPC is the SWA sheath, particularly on TPN circuit. As long as the sheath CSA is considered and banjo'd with a fly lead to earth terminals in DB's and accessories then it is very acceptable.
 
This Q&A comes up all the time,regarding Swa as a cpc/main earth bond conductor.
The obvious answer Swa maybe ok for a cpc,but not for Mebc.
This situation is happening all over the place,installing Swa’s without regard for main Earthing/Mebc.
It’s how we get over it is the hardest part,especially if the installation is in service for years,without anyone reporting,it does not comply.
Who is actually gonna install another Mebc to the supply,how,who pays etc..can be a nightmare.
 

Reply to the thread, titled "Feeder pillar query" which is posted in Commercial Electrical Advice on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top