Hmmmyou should never rely on using the armoured wiring has a CPC.
specially 3 phase .
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Feeder pillar query in the Commercial Electrical Advice area at ElectriciansForums.net
Hmmmyou should never rely on using the armoured wiring has a CPC.
specially 3 phase .
ThanksThe Feeder Pillars I have worked on, relied on the sheath, be it SWA or some other armouring (not sure it was a long time ago) as the main earth conductor, you would need to look at SWA data to find out the CSA of the armour and then decide, if it's large enough in CSA to act as a Main Earth and a Bonding conductor, Atatched table is all the info I have, may help.
Hi.The water pipe comes out of the ground in plasic then changes to copper after the stopcock then about 2 foot later terminates in a garden type tap...all inside the enclosure.Is the water pipe metal or plastic.
Hi.The water pipe comes out of the ground in plasic then changes to copper after the stopcock then about 2 foot later terminates in a garden type tap...all inside the enclosure.
I suppose what I'm trying to figure out is if it is an extraneous conductive part..(dont think so.)is it exposed conductive part (doubt it)so then it doesnt require equipotential bonding..If it was copper coming out of the ground it would be different.(I don't know now if it even needs the 6mm)
The other item is the cabinet itself I suppose it could become live under fault conditions but should it need an additional bond in addition to the CPC?? I cant think why it would.
Thanks for your thoughts
you should never rely on using the armoured wiring has a CPC.
specially 3 phase .
More often than not CPC is the SWA sheath, particularly on TPN circuit. As long as the sheath CSA is considered and banjo'd with a fly lead to earth terminals in DB's and accessories then it is very acceptable.you should never rely on using the armoured wiring has a CPC.
specially 3 phase .
you should never rely on using the armoured wiring has a CPC.
specially 3 phase .
if fault current that accrues on a system, if SWA is damaged at some point then it is dangerous then you are relying on the SWA to clear that fault .Why not?
in any fault current that accrues on that system and if SWA is damaged at some point then it is dangerous then you are relying on the SWA to clear that fault .
how would you know !If the cable is damaged then it is not fit for purpose anyway
how would you know !