Hi.I've got a couple of queries regarding feeder pillars on a car park I an working at.
There are 3 pillars.All are metal.No 1 is supplied by 70mm 4 core xlpe swa.3 phase and neutral.cpc/bond is the swa.
No 2 is 25mm 4 core. And No 3 is 70mm 4 core. No 2 & 3 pillars also have water supply in a separate compartment.The installation is TN-S..I'm wondering should there be an earth bond run back to supply DB in main building or is the swa sufficient..The main buildings neutral is 150mm (ish) and the main bonds inside the building are 50mm.
There are 3 pillars.All are metal.No 1 is supplied by 70mm 4 core xlpe swa.3 phase and neutral.cpc/bond is the swa.
No 2 is 25mm 4 core. And No 3 is 70mm 4 core. No 2 & 3 pillars also have water supply in a separate compartment.The installation is TN-S..I'm wondering should there be an earth bond run back to supply DB in main building or is the swa sufficient..The main buildings neutral is 150mm (ish) and the main bonds inside the building are 50mm.