Agreed. I just wondered what others do as I do a quick I&T before I commence the work, but I know others "gamble" on it being all okay.

Just out of interest what is meant by "global L + N to Earth"? Are you merely meaning you only do L + N to E 250v IR rather than also doing L to N on each circuit?
 
Agreed. I just wondered what others do as I do a quick I&T before I commence the work, but I know others "gamble" on it being all okay.

Just out of interest what is meant by "global L + N to Earth"? Are you merely meaning you only do L + N to E 250v IR rather than also doing L to N on each circuit?

Installation isolated, link L+N linked at the dead side of main switch or where ever convenient, all fuses present or MCBs on and test to E, 250V soft test first if ok then 500V, thus testing the whole lot in one, this will show anything major up, I switch all of the lights on first.
Sometimes I link L to N with my test plug (rest as above) plugged into a S/O and do it that way, depends on whatever is easier.

Sometimes I will do more or less tests depending on what I find, no need to start stripping the whole lot down or go on major fault finding exercises at this stage, I forgot to add above that I also do a quick Zs test at a random socket both up and down (if separate :) ).

This combined with a visual and you can usually tell pretty quickly if you are going to have major problems or not.
 
Suitable tests to give you an indication that you don't have any pre-existing faults or a shared neutral situation between up and down stairs lighting circuits. Failure to do pre-testing can lead to a whole lot of problems on a CU change with RCD's tripping etc.

And typically just as you were thinking of or looking forward to going home too... lol!!



There speaks the voice of (bitter) experience!! :)
 
crack on m8 every tom dick or harry is having a go anyway ,Part **** is a joke.
we,ve all see the thousands of prosecutions for failing to notify building control.
every year i wonder why i bother paying for this shambles
Calm down, it is only a rugby match :biggrin:
 
Or even worse, I've seen the RCD installed but unresponsive, some nugget had actually cracked it in half along the seam of the casing and bodged a piece of 16mm cable to bridge the top and bottom. And TAPED it together.
At least they made an effort. I've seen a few times an RCD in the board just bypassed because 'they' didn't know what to do!
 

Reply to Fitting new consumer board - no part p? in the Talk Electrician area at ElectriciansForums.net

Similar Threads

I should have written more…. 😫 😂😂
Replies
5
Views
1K
  • Question
Seems like he's using the best method for that particular board
Replies
6
Views
1K
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
1K
Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
537
  • Question
Unfortunately they will not respond in writing, this came about because I threatened to complain to the NICEIC
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks