Hello there, Is there any regulation regarding the use of flex in consumer units. eg. Can a 1.5 x 3core be used as a supply cable from an 6a mcb to a fused spur feeding downlights? I came across this the day and I was curious if it was within the regs. Thanks for your time.
 
It would never have occured to me to use flex for fixed wiring, but I'd be interested to hear why its classed as rough. I'm assuming its because its stranded so more prone to damage, strands breaking etc and affecting CCC?
 
Use of flexible cables
521.9.1
A flexible cable shall be used for fixed wiring only where the relevant provisions of the Regulations are met. Flexible cables used for fixed wiring shall be of the heavy duty type unless the risk of damage during installation and service, due to impact or other mechanical stresses, is low or has been minimized or protection against mechanical damage is provided.
NOTE:Descriptions of light, normal and heavy duty types are given in BS 7540.

is it just me or do the regs not make much sense most of the time
 
I did quote a reg number on a previous thread about Flex actually, It started to get heated LOL, Basically it is allowed but like E54 and many others here think it is the wrong cable for installs and it should only be used from a spur to an appliance.
 
I wonder how factories wired in SY, CY and YY haven't burnt to the ground yet....

Must be just luck. The next time I do a job at a factory with multiple drives, valves and instrumentation I'm going to wire it all in twin and skin just to be sure.
 

Reply to Flex in a consumer unit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
782
This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
721

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top