Do you need to mention that the PV has no RCD, and being a TT system it is usually a requirement?
Just for advice, if there is no AC supply to the inverter then there would be no AC coming from PV system, an inverter can take 5 seconds to shut down though, hence why they should never be on a 'shared RCD', but the DC would still be live, well in the daytime of course...
 
Do you need to mention that the PV has no RCD,
looks to me like it's got an RCD in the garage unit.

looks about right TC, and now I've seen the photos I realise what you meant by connected at the suppliers fuse, not quite as bad as I'd pictured it (I'd been imagining 2 sets of tails somehow wedged in to the same hole).

bit of a dogs dinner, and the customer is definitely loosing out on the free leccy (which if it was rent a roof, then that is the only benefit they've be getting from the system, so just a bit important), but I think you've got the levels about right, though I agree that the C2s probably are borderline between 2&3.
 
Do you need to mention that the PV has no RCD, and being a TT system it is usually a requirement?
Just for advice, if there is no AC supply to the inverter then there would be no AC coming from PV system, an inverter can take 5 seconds to shut down though, hence why they should never be on a 'shared RCD', but the DC would still be live, well in the daytime of course...
PV has got RCD protection, main fuse to 63A RCD, 20A breaker see pictures. Unless you mean up in the roof space?

Edit 63A 30mA rcd
 
looks to me like it's got an RCD in the garage unit.

looks about right TC, and now I've seen the photos I realise what you meant by connected at the suppliers fuse, not quite as bad as I'd pictured it (I'd been imagining 2 sets of tails somehow wedged in to the same hole).

bit of a dogs dinner, and the customer is definitely loosing out on the free leccy (which if it was rent a roof, then that is the only benefit they've be getting from the system, so just a bit important), but I think you've got the levels about right, though I agree that the C2s probably are borderline between 2&3.

Maybe put down C 2.5:wink5:
 
tbh, I've not done any of the new reports, so you'll know better than me what to put down I reckon.
 
here's one I did earlier!View attachment 12609 Not the best I've ever done but the only photie I've got to hand.
labels went on later before anyone comments!
Middle set of tails go to dedicated CU. Right hand tails (as we look at it) go to main CU

Moggy, make sure you don't strip the outer sheath of the tails outside of the henley block otherwise you have a single insulated conductor with no mechanical protection outside of an enclosure which would warrant a defect code on an EICR.
 
HEY TC,

good pic! tails are undersized for 100amp suppliers fuse

The 20A MCB within the 2 way consumer unit would provide overload protection for the 16mm2 tails so not an issue though connecting before the suppliers meter is a serious no-no!
My 2 way solar CU is supplied with 10mm2 tails and that's not an issue either.

Absolute shocking job though. I'm just amazed somebody could actually carry out an installation like that and not give it a second thought :(
 
I think I have spotted another fault here chaps, they have brought the Earth in from the array, so bringing a potential into the equipmental zone, it should be on its own Earth spike, unless there are velux windows of course, which I doubt. Your thoughts?
I did not spot the RCD though, sorry.
[ElectriciansForums.net] From a non solar guy, does this look OK
 
All looks like cheap tat as well, probably won't last more than a few years!

Think that's the roughest solar electrical install i've seen, I wonder what the roof work is like...
 
All looks like cheap tat as well, probably won't last more than a few years!

Think that's the roughest solar electrical install i've seen, I wonder what the roof work is like...

they keep popping up on this forum, i reckon there hundreds out their like this one and its only time before we all start picking up repair work for mis sized inverters, poor wiring, panels slipping. The trouble with that install also is were was the persons pride? who in the right mind leaves a job like that, yes ok im not proud of all my jobs, but even in my early days i wouldnt leave anything like that!
 
Moggy, make sure you don't strip the outer sheath of the tails outside of the henley block otherwise you have a single insulated conductor with no mechanical protection outside of an enclosure which would warrant a defect code on an EICR.

Hey Gaz?

Does that include all tails in and out of the meter and main head too? As 95% of the instals i go to obviously dont now comply to the new EICR.
So?
Does that mean i have to make all necessary changes to the tails to make the instal/electrics comply?

Thanks

Fiardor
 
It's always been the case that you can't have a single insulated conductor outside of an enclosure or containment but you're right, there's many installs out there with that issue and the DNO are more guilty than most, especially with their meter terminations. Maybe that's where the habit has come from?
If you're carrying out an EICR then just report and code them appropriately. No need to make any changes there and then, only if the customer chooses to have the defects rectified though the meter terminations are obviously the DNO's responsibility. You can still note them on your EICR though.
 
It's always been the case that you can't have a single insulated conductor outside of an enclosure or containment but you're right, there's many installs out there with that issue and the DNO are more guilty than most, especially with their meter terminations. Maybe that's where the habit has come from?
If you're carrying out an EICR then just report and code them appropriately. No need to make any changes there and then, only if the customer chooses to have the defects rectified though the meter terminations are obviously the DNO's responsibility. You can still note them on your EICR though.

Duly noted thanks Gaz

And will from now on adhere to the new EICR. (mostly) LOL
 
I think tails are undersized for 100 amp suppliers fuse

If there's a 20A MCB in the 2 way CU then how can the tails be subjected to an overload greater than the rating of the MCB?
In other words, the MCB is your overload protection and the tails are fine.

Think of an 800A busbar chamber with a few 32A switch fuse isolators fed from it. Would you expect conductors rated at 800A to be terminated into the 32A switch fuse?
 

Reply to From a non solar guy, does this look OK in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
814

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
702
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top