If there's a 20A MCB in the 2 way CU then how can the tails be subjected to an overload greater than the rating of the MCB?
In other words, the MCB is your overload protection and the tails are fine.

Think of an 800A busbar chamber with a few 32A switch fuse isolators fed from it. Would you expect conductors rated at 800A to be terminated into the 32A switch fuse?
If the RCD short circuited then the prospective fault current could be thousands of Amps.
Agree to a point about a busbar chamber but the small tails would or should be mechanically protected.
 
They are mechanically protected - by their outer sheath. No other protection needed, subject to environment.
Many thousands of amps would be great for fast breaking of a protective device that's suitably rated to break the fault current without destroying itself.
 
yes, it will only have electricity he is using pass through it. the excess will go off to the grid so I'm not right in saying he will be charged for everything he generates. As you say, just no reduction in his bill!
 

Reply to From a non solar guy, does this look OK in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
814

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
702
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top