A small under counter AEG fridge. Instructions say it is fitted with a 13A fuse in the plug. Also states it must be replaced by a 13A fuse. The fridge is drawing 0.32 amps. A 13A fuse is ridiculously oversized. If having a mcb or RCBO at the CU for just the fridge, a 1.00mm cable can be run on a radial for it.

The instructions do say that a qualified or competent electrician must fit the appliance, so a get out for them. If the electrician say 3A will do then that is that I suppose. Do many ignore these types of instructions and say insert a 3A fuse in the plug? Safer.
 
No reg says local isolation is needed.
You should work to your electrical training and knowledge, not be like one of these, rear end covering, moronic, reg followers.

Show me the reg that says local isolation is mandatory? Whatever local isolation is of course. Where should this non-mandatory local isolation be? in a cupboard? Over a worktop? In an adjacent utility room? Under an appliance? Where?

We are talking about you saying that 1mm is 'electrically correct' for the circuit. Don't try and change the subject because you are wrong and know it mate. Have a look at the table I mentioned in a previous post for the reg.
 
We are talking about you saying that 1mm is 'electrically correct' for the circuit. Don't try and change the subject because you are wrong and know it mate. Have a look at the table I mentioned in a previous post for the reg.
A sole appliance, on a radial, drawing a third of an amp, on 1.00mm cable on say a 10A mcb is electrically sound and safe. Are you saying it is not?
 
We are talking about you saying that 1mm is 'electrically correct' for the circuit. Don't try and change the subject because you are wrong and know it mate. Have a look at the table I mentioned in a previous post for the reg.
You are supposed to be electrically trained. To think. Now do not look at table. Tell me where it is electrically not sound or safe? I will be waiting a long time.
 
I understood it last time. Gave up trying to argue though. You wouldn't listen to anyone elses opinion.
Clearly whoever they are this person possesses more intelligence and common sense than the rest of us, not to mention the persons making up the JPEL/64 committee. It’d be easier if we all just bow down to the superiority of their arguments and accept their word as truth instead of following the clearly illogical and inferior regulations that have gotten us to this point...

Sisyphus had an easier task than reasoning with this one.
 
A sole appliance, on a radial, drawing a third of an amp, on 1.00mm cable on say a 10A mcb is electrically sound and safe. Are you saying it is not?
You are supposed to be electrically trained. To think. Now do not look at table. Tell me where it is electrically not sound or safe? I will be waiting a long time.

Again mate, don't change the subject. I did not mention 'safe' in any of my posts.
Quoting you: "1.00mm would not be electrically incorrect." Post #69.
This is incorrect. 1.00mm is electrically incorrect. Look at the regs.
 
A quick scan of the lengthy thread and diving back to the original discussion here, most appliances with a 13amp plug top are what we class as fixed current equipment and therefore do not need overload protection and this is why we can see fuses rated higher than the CCC of the flex that supplies the unit, if the manufactures guidance requests a lower fuse rating then that is what should be fitted but the likes of appliances with motors often have a 13amp fuses covering flexes that have a lower CCC simply to allow for inrush where the common 5 or 3 amp rated could periodically nuisance fail, you can argue that you fitted smaller fuses with little or no issue but when millions of products are sold then the industry may see a reflective % of these nuisance popping which requires extra staffing to their help lines and unnecessary costs may also be put on the user, these and many other reasons are why we don't always fit the lowest rated fuses that we could theoretically get away with.
The exemption from overload protection can be applied to most household hard wired circuits if necessary but common practice and rule of thumb often doesn't see us doing that, one of the few circuits that is classed as a variable load and needs to have a max rated fuse for O/L protection is a ring main for obvious reasons that there is no max current demand that we can calculate as it is an unknown variable, other regulations can also interfere with front end fusing like lighting circuits where the lamp-holders themselves can specify a max fuse rating for the circuit it is on.-
 
Again mate, don't change the subject. I did not mention 'safe' in any of my posts.
Quoting you: "1.00mm would not be electrically incorrect." Post #69.
This is incorrect. 1.00mm is electrically incorrect. Look at the regs.
A reg quoter again. Lokks like someone who has been trained. I told you not to look at regs, then assess, then tell me where it is not electrically sound and not safe. I am still waiting.
 
A reg quoter again. Lokks like someone who has been trained. I told you not to look at regs, then assess, then tell me where it is not electrically sound and not safe. I am still waiting.

You have a very strange attitude. You remind me of the antivax type people with the way you argue and refuse to listen to reason.

There will always be cases of things that are electrically sound, but don't necessarily comply with BS7671. The regs cannot cover every eventuality. You are free to do things that don't comply, as long as you justify your deviations.
 
a 13amp plug top are what we class as fixed current equipment and therefore do not need overload protection
Assuming there is no fault of course. In a fault condition it may draw more current than it is designed to, with a fire/electrocution risk. That is where correctly sized overload protection comes in - to nip the danger in the bud.

I have seen enough innards of burnt out appliances that would have benefited in safety aspects having a correctly sized fuse in the plug, with 13A being far too high.

Your point about manufacturers increasing fire/electrocution risk because of profit is relevant.
 
Last edited by a moderator:
You have a very strange attitude. You remind me of the antivax type people with the way you argue and refuse to listen to reason.

There will always be cases of things that are electrically sound, but don't necessarily comply with BS7671. The regs cannot cover every eventuality. You are free to do things that don't comply, as long as you justify your deviations.
Did you understand what I wrote? Looks like you never.
I told him not to look at regs, then electrically assess, where an appliance with a current draw of 0.3A on a dedicated radial, with 1.00mm cable with 10A mcb. I asked him to tell me where it not safe. He continually spouted the regs, unable to assess it, and still has not.

The scenario I gave is 100% safe. The regs say minimum of 1.5mm for power, which is good practice. There is a reason why they set that. So as the hard of thinking do not cause fires.

Electricians are trained to follow procedures and regs - think inside the box.
Graduate engineers are educated to think - promoting outside the box thinking. That is why the British are very inventive. Training and education are different. The British system does differentiate between the two.
 
Last edited by a moderator:
Did you understand what I wrote? Looks like you never.
I told him not to look at regs, then electrically assess, where an appliance with a current draw of 0.3A on a dedicated radial, with 1.00mm cable with 10A mcb. I asked him to tell me where it not safe. He continually spouted the regs, unable to assess it, and still has not.

The scenario I gave is 100% safe. The regs say minimum of 1.5mm for power, which is good practice. There is a reason why they set that. So as the hard of thinking do not cause fires.

Electricians are trained to follow procedures and regs - think inside the box.
Graduate engineers are educated to think - promoting outside the box thinking. That is why the British are very inventive. Training and education are different. The British system does differentiate between the two.

Please listen to people.

He isn't saying it is not safe. He is saying that it doesn't comply with the regs.

And as I say, there are many circumstances which may be safe, but which do not comply with the regs. The regs cannot cover every eventuality.

And give it a rest with the bold text - it's very patronising and completely unnecessary.
 
Please listen to people.

He isn't saying it is not safe. He is saying that it doesn't comply with the regs.

And as I say, there are many circumstances which may be safe, but which do not comply with the regs. The regs cannot cover every eventuality.

And give it a rest with the bold text - it's very patronising and completely unnecessary.
I know that.

He wrote: "You also talked about using an incorrect cable size."
The cable size was not incorrect, it was perfectly suitable and safe. Not conforming to a reg is another matter. He could not figure out the difference.

I did listen, with a lot of narrow minded nonsense coming from some. They should do the listening, not me. Darkwood came out with one of the few sensible replies.
 
Last edited by a moderator:
I know that.

He wrote: "You also talked about using an incorrect cable size."
The cable size was not incorrect, it was perfectly suitable and safe. Not conforming to a reg is another matter. He could not figure out the difference.

I did listen, with a lot of narrow minded nonsense coming from some. They should do the listening, not me. Darkwood came out with one of the few sensible replies.
I will close this if you continue with your current attitude.
 
A reg quoter again. Lokks like someone who has been trained. I told you not to look at regs, then assess, then tell me where it is not electrically sound and not safe. I am still waiting.

You really don't like being wrong. ???
How can I tell you that your idea of using 1.0mm cable is not 'electrically correct' if you don't want me to point you to something, like the regs... You make no sense what so ever.
I'm not sure what you are waiting for, you are wrong, deal with it. ?
You are doing great at getting your post count up quickly though, I will give you that..
 
Electricians are trained to follow procedures and regs - think inside the box.
Graduate engineers are educated to think - promoting outside the box thinking. That is why the British are very inventive. Training and education are different. The British system does differentiate between the two.

Perhaps this discussion would be better held on a 'Graduate Engineer's forum', although I suspect more than one graduate engineer has participated in this thread.

Your opening post states "If having a{sic} mcb or RCBO at the CU for just the fridge, a 1.00mm cable can be run on a radial for it." This may be technically correct (or it may not, depending on factors that haven't been disclosed), but from a regulatory perspective it would not be permissible.

Given that this is an 'Electrician's' forum, it might be an idea to make clear when you wish to set regulations to one side and discuss hypothetical situations. Otherwise such arguments can appear to be pointless polemic pedantry, to the casual observer, or may be taken at face value by a hapless DIYer who happen to stumble across this thread in their quest for information.
 
Suppose the OP had written the post as follows:

'Possible justification for deviating from MI's regarding fuse rating'
A certain fridge is supplied with a 13A fuse in the plug and the MI's state that this size is to be used. However, the consumption is low, a fraction of an amp when running, and I suspect even the stall current would not blow or even stress a fuse of much lower rating, maybe even as low as 3A. Therefore, although the unit presumably conforms to the applicable standards as-is with a 13A fuse and would be regarded as safe, deviation from the MI's to use a smaller fuse might yet add marginally to its safety in the event of certain types of fault. For example, reducing the risk of fire in the event of motor failure and gross overcurrent that the internal thermal protection does not successfully disconnect, or reducing the energy dissipated at a short-circuit fault. Given the disparity between the actual current and the implied need for a 13A fuse, and the fact that any reliability disadvantage from using a smaller fuse is one of lost functionality rather than reduced safety, I contend that it is a good example of where the application of technical knowledge can enhance safety compared to slavishly following MI's.

On the same subject although not enhancing safety, subject to Zs and VD, the appliance could manifestly run from its own dedicated circuit wired in 1.0mm² on say a 10A MCB. Yet BS7671 requires the cable to be a minimum of 1.5mm² on account of it being a 'power' circuit, despite carrying lower load than many lighting circuits.



I think more of us might have agreed.

Of course, the whole thing rests on the stall current, which means one of use has to hook an ammeter in series with a fridge and twiddle the thermostat while it's running to stall the compressor.
 
Ghost Ship for me. Not too many though, early start tomoz. 3 should be safe, 13 would be too many.
 
Not may, it is. The statement by me was to point out how low the current draw was on the fridge.

Without full details of the circuit in question, it was impossible to determine whether or not your point was technically correct.

Was that 1mm circuit 30' or 30 miles in length? Sorry, but your original comment provided insufficient data to make such a determination. That's how this works, right?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Fuse too big on fridge
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
120
Unsolved
--

Advert

Thread statistics

Created
John-SJW,
Last reply from
Darkwood,
Replies
120
Views
17,819

Advert

Back
Top