claypole
One scenario where G83/1 compliance and FIT band are clearly distinguished is where 3 phase is involved. G83/1 clearly allows you to output at 16A per phase, whilst the corresponding power output would obviously take you above the 4kw FIT band. I've been following this thread with interest and coming more and more round to the view that it is the inverter output that counts in both instances. For one thing, it is impossible to give a maximum output (dc) from an array. The sizes commonly referred to are only a nominal rating under test conditions. The manufacturing tolerance for most panels is +10% so the array output under std test conditions could already be 10% higher. If you then add cell temperatures below 25c or irradiance above 1000 the output could be higher still - how could you possibly define the max? The G83/1 certified inverter on the other hand is hard set to output maximum 16A. For G83/1 "fit and inform" surely this is the only information you need? Where it gets complicated is if you decide to make an application in advance because this form will ask for kva capacity. I would still say this figure is also governed by the inverter because again you can't give a definitive maximum output from the array. The Sunny Boy 4000TL supplied to UK is preset to comply with G83/1, maximum 16A and maximum 4000kva (which presumably would only occur when grid is at 250V). But why would you make a pre-application if your inverter is certified G83/1? I can see why people consider a nominal array >4kw is relevant due to the TIC / DNC questions on the FIT registration but surely in the case of the Sunny Boy 4000TL (and doubtless others, it's just that I'm only looking at this inverter) you can rightly declare both TIC and DNC as 4kw?