It is not clear how the switching is carried out. Six fluorescents, four each with one way switches and two each with two two way switches.
However that is not how I read the controls and it seems that there is a 'master' switch at the front door for what are the access lights. Check this switch and if it is double poled i.e. switching live and neutral it may just be the slightly different opening or closing times of each pole which is the problem (you get a parallel path during this period which may be sufficient to trip the RCD)
However that is not how I read the controls and it seems that there is a 'master' switch at the front door for what are the access lights. Check this switch and if it is double poled i.e. switching live and neutral it may just be the slightly different opening or closing times of each pole which is the problem (you get a parallel path during this period which may be sufficient to trip the RCD)