Ge rcbo | on ElectriciansForums
Discuss Ge rcbo in the UK Electrical Forum area at ElectriciansForums.net
bartkusal
London
Hi all,
Just a quick one, can anyone advice where I can get General Electric 6A 30mA RCBO type B, looked on int. couldn’t find, just type C. Seems that it very unpopular. Alternatively, what other RCBO will fit that board, the board was installed in 2000, it is a split board, only half protected by RCD, and I am working on the lighting circuit which is not.
Thanks in advance for your help.
Regards: Al
Its domestic, don’t see the need of type C, and not sure if I would satisfy the max Zs values for that type, because I quickly checked the Zs on the socket to give me a picture of the earth, and it was 0.89, so if the mcb protecting it would be 32A type C instead of B, from top of my head I think that is over the max allowed, it could be the same on lighting circuit too. I don’t want to go that way where some say if rcd protected the max Zs is 1667ohms or whereabouts, not my cup of tea, sorry...
Reply to Ge rcbo in the UK Electrical Forum area at ElectriciansForums.net
My thoughts exactly! Snowed under with work at the moment, so might have to pass it on 😬😬
Sockets will probably be ok on one, a little inconvenient in the event of a fault though, I'd probably like a 7th rcbo in. Wonder if hes linked...
7K