i am well and truly confused now.great are 'nt they abbreviations. yesterday i drove my m.p.v to do a p.i.r on an install it was wired in p.v.c and some old v.i.r had some good Zs's tho.Not sure on some cable sizes as g.a.t.s was not taken into calcs da da da lol only joking guys.I know are my few brain cells right in telling me right that m p b is main ? bond and s b c is supplementary bond connection.Has the figure gone from 0.05 to .005 and not sure what figure i am looking for & what i am testing now.genuinely all help is appreciated this game is certainly ambiguous ain't it
just to clarify i was refering to question (1 ) testing if extraneous conductive are adequate by testing with an insulation resistance tester and long leads and does not meet requirements if >22Kohms i was just using the long lead r2 method were you refering to an r1+r2 method which does not apply to this situation?
Hi Chris - very interesting. I'm aware that brb does not specify resistances. I had this very sort of discussion with the tutor who was teaching me the 2391. I was saying so what if a mpb conductor had to be 30metres long , that would put it over 0.05Ω he said you would have to increase the csa.
It a common misconception, i remember my 2391 trying to tell us this, i explained to him he was incorrect, if you read GN3 carefully you will see that its not placing the 0.05 on the overall length. As i said above the nic also gave the same advice, so i explained and they agreed.
AFAIK the brb does not ask you to test mpb conductors if you can visually confirm continuity. However, if you can not visually confirm continuity a test would have to be done. What result would you be looking at if you were testing between a gas and water pipe (two extraneous-conductive-parts) - isn't gn3 suggesting it should be this 0.05 value?
GN3 is referring to where say the structural steel is used as a bonding conductor for example and can not be removed, testing between two points the resistance should be no more than 0.05.
What your looking to achieve is to limit the touch voltage, so you could use the equation used for effectiveness of supplementary bonding as this is in effect what your trying to achieve. That would need to bee one hell of a length of of cable between two points especially when the minimum is 6mm.
edit : reading gn3 again 2nd bottom paragraph P35 it talks about using test method 2 where the bonding clamps have been "built in" then connect across extraneous-conductive-parts and check for the 0.05 value. The extraneous conductors could be gas and water? I don't know why it doesn't say between
extraneous-conductive-part and the MET
Well its referring to any two points, this could be two of many in one given installation.
Are you and IQ talking of supplementary protective bonding conductors ? Surely they connect between an exposed-conductive-part and an extraneous-conductive-part?
Im talking about Main protective bonding though in principle your trying to achieve the same as supplementary bonding conductor limiting touch voltage.
Oh and yes the figure is 0.05 ohms my typo sorry
[
GN3 is referring to where say the structural steel is used as a bonding conductor for example and can not be removed, testing between two points the resistance should be no more than 0.05.
Pushrod, i dont have my GN3 to hand, but does it mention simultaneous?
I took the "eg where bonding clamps have been 'built in'. " just to mean that access to the clamps on MPBCs was restricted, ie behind panelling. Definitely see that you could be quite correct though.
No nothing at all in this section about that, or being able to touch at same time. [That is why i was wondering about distant gas and water pipes where clamps might not be accessible] .
No nothing at all in this section about that, or being able to touch at same time. [That is why i was wondering about distant gas and water pipes where clamps might not be accessible] .
Hi Please could you give some guidance on the maximum length of a Main protective Bonding Conductor. People mention the 0.05, though the only reference is in GN3, though this reads as a test between two points where the bonding connection is say structural and not applied to an overhaul length. The regs only mention the CSA. Now we are trying to limit touch voltage, so is there a fundamental calculation which may be used? Many thanks Chris
The length of main bonding conductors is not normally something that needs to be considered in most installations Chris. The maximum touch voltage between extraneous conductive parts for general installations is 50v (some special locations are limited to 25v). You would have to have a very long main bonding conductor to get that kind of voltage drop.
Hence the equation 50/Ia