Robbie what is the trip rating in mA of the RCD part of your RCBO ?
The max Zs values for RCD's RCBO's depend on the mA rating, and are as follows:
30mA = 1667 ohms
100mA = 500 ohms
300mA = 167 ohms
500mA = 100 ohms
So your Zs values will be fine
The OCP part requires more thought, as your Ze values are low, it is the (R1 +R2) values which are giving the higher part of your readings.
If it is a TN system and a distribution circuit, a 5 second disconnection time will be allowed.
As a 25 A C type OCPD will require 250 A to operate instantaneously, 10 X 25A , 230/250 = 0.92 ohms, but if you are allowed a disconnection time of 5 secs this can be higher.
Edit; I have not included any correction factors here for clarity