good evening,
just looked at a job where a glass washing machine is to be installed in a factory.
3 phase crabree board already there. plenty of spare ways and only load on the ccu is power and lighting and alarm system.
job request from customer, need a commando socket adjacent to drain to plug machine in.
the way i would install would be, three phase board 63a 3 phase breaker.
16mm to a 63a mem switch fused isolator next to board. from there run a 16mm 5 core armoured clipped direct around 45m to commando socket.
another electrician has quoted and subsequently come in cheaper as said 4 core 16mm.
and no mention of a 63a fused isolator?
advice chaps?