glasgospark

self employed spark had fitted rcd protected DB to replace 3036 board

after fitting everything plugged in to a socket and turned on would trip rcd , on both rings and when the heating switched on

declined the job to busy and KNACKERED/GRUMPY today but wondering what you guys think , it was a rcd main switch so no dual rcds to worry about getting neutral in the right bar
 
Did the 'self employed spark' not properly inspect + test and issue an EIC when doing the board change?

Nothing should be tripping if he had done the job properly.

Guaranteed the 'spark' can't sign his own work off - so the likleyhood of their being an EIC is probably nill.
 
self employed spark had fitted rcd protected DB to replace 3036 board

after fitting everything plugged in to a socket and turned on would trip rcd , on both rings and when the heating switched on

declined the job to busy and KNACKERED/GRUMPY today but wondering what you guys think , it was a rcd main switch so no dual rcds to worry about getting neutral in the right bar

So its a non compliant board too them?
 
Was first fixing a kitchen today and got talking to the homeowner, and he said they had there house rewired last year. However when i was stripping out the old sockets they were red/black cables so i asked the extent of the rewire and they said complete rewire to which i showed them the old cables. They were not shocked because apparently the guy fitted a double socket in the hallway but didnt run any cables to it just screwed the front on so they thought it worked, i didnt think at the time but should of asked about certs
 
Was first fixing a kitchen today and got talking to the homeowner, and he said they had there house rewired last year. However when i was stripping out the old sockets they were red/black cables so i asked the extent of the rewire and they said complete rewire to which i showed them the old cables. They were not shocked because apparently the guy fitted a double socket in the hallway but didnt run any cables to it just screwed the front on so they thought it worked, i didnt think at the time but should of asked about certs

Hahaha!

Maybe it was bluetooth.
 

Reply to got a call today in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
351
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top