Had a call out late last night, everytime the shower comes in it's blows the whole house.

The set up of the board is duel rcd. 2 mcb either side.

Cooker/shower on left

Lights/sockets on right



So the power to the shower switch is fine, again this can function fine and send power to the shower, bit as soon as the shower is pressed is wipes both rcds straight out after 2seconds.

I did a insulation resistance test, was getting 0.25megohms.
Removed tge switch and was getting 459megohms. So thought new switch, put new switch on and still wiping the whole board out, but obviously were not getting a dead short as the power to the shower is fine untill pressed.

Quite interesting this one. But such a obvious one which I will always look out for on my future PIRs
 
Me too, this wipe the whole lot out, rcds & mcbs, bridge you bus bars on a install and see for yourself.

Tony, due you think moist air that another member mentioned could contribute to this?
 
There was no continuity between neutral & earth and untill the shower is switched on from the body of the shower not the iso switch then we are all good and no tripping. But when the shower was activated both rcds and all 4 mcbs blew.
 
A residual-current device (RCD) is an electrical wiring device that disconnects a circuit whenever it detects that the electric current is not balanced between the energized conductor and the return neutral conductor.

In a pme system the neutral will be at the same potential
 
Obviously it's not jumping that If no one is taking a shower, but as soon as the button is press it will drawn power from that board....(same as sometimes you see a flash in a light switch when pressed) how far can that jump at the very moment the shower draws power?
 
Obviously it's not jumping that If no one is taking a shower, but as soon as the button is press it will drawn power from that board....(same as sometimes you see a flash in a light switch when pressed) how far can that jump at the very moment the shower draws power?


That is an arc that's being drawn across two contacts, normally when being switched Off. Not the same thing as two static bars and an arc jumping across them....
 

Reply to Guess the fault in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
989
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top