Had a call out late last night, everytime the shower comes in it's blows the whole house.

The set up of the board is duel rcd. 2 mcb either side.

Cooker/shower on left

Lights/sockets on right



So the power to the shower switch is fine, again this can function fine and send power to the shower, bit as soon as the shower is pressed is wipes both rcds straight out after 2seconds.

I did a insulation resistance test, was getting 0.25megohms.
Removed tge switch and was getting 459megohms. So thought new switch, put new switch on and still wiping the whole board out, but obviously were not getting a dead short as the power to the shower is fine untill pressed.

Quite interesting this one. But such a obvious one which I will always look out for on my future PIRs
 
Akabarthesta I didn't buy, nor fit the board, I'm just the guy who was called to sort the issue.

Also the nuetrals were fine, it's the live that was tge problem with the arc from the bus bar.
 
having given the matter considerable thought, i think an analogy would best explain the phenomenon, something similar to comparing electricals with water. the pressure is the voltage or potential difference, and the flow is current or electron movement.

so... say that the one busbar is the entrance to harrods, and the other to harvey nicholls. the current ( women shoppers ) moving in and out of both entrances is steady and continuous. now : harrods announce a sale. ( switching the shower on ). suddenly the flow of electrons through harrods door becomes a mad rush, and seeing this, the women ( electrons) going into harvey nicholls sees the rush and jump across to the harrods entrance. this causes a massive inbalance in both sets of customer ( electron) flow causing the revolving doors to come off their hinges ( RCD s trip).

hope the above clarifies the situation.
 
having given the matter considerable thought, i think an analogy would best explain the phenomenon, something similar to comparing electricals with water. the pressure is the voltage or potential difference, and the flow is current or electron movement.

so... say that the one busbar is the entrance to harrods, and the other to harvey nicholls. the current ( women shoppers ) moving in and out of both entrances is steady and continuous. now : harrods announce a sale. ( switching the shower on ). suddenly the flow of electrons through harrods door becomes a mad rush, and seeing this, the women ( electrons) going into harvey nicholls sees the rush and jump across to the harrods entrance. this causes a massive inbalance in both sets of customer ( electron) flow causing the revolving doors to come off their hinges ( RCD s trip).

hope the above clarifies the situation.

Gosh, things must be going well in Cheshire if Harrods and Harvey Nichols are at the fore front of your mind! LOL
 
having given the matter considerable thought, i think an analogy would best explain the phenomenon, something similar to comparing electricals with water. the pressure is the voltage or potential difference, and the flow is current or electron movement.

so... say that the one busbar is the entrance to harrods, and the other to harvey nicholls. the current ( women shoppers ) moving in and out of both entrances is steady and continuous. now : harrods announce a sale. ( switching the shower on ). suddenly the flow of electrons through harrods door becomes a mad rush, and seeing this, the women ( electrons) going into harvey nicholls sees the rush and jump across to the harrods entrance. this causes a massive inbalance in both sets of customer ( electron) flow causing the revolving doors to come off their hinges ( RCD s trip).

hope the above clarifies the situation.

Not if they have just popped out from Ascot to load up with extra shampoo (resistance to current flow caused by large brimmed hats and the blocked revolving doors) :alucard: :jester: :indian_chief: :party:
 

Reply to Guess the fault in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
989
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top