p11jor
Had a call out late last night, everytime the shower comes in it's blows the whole house.
The set up of the board is duel rcd. 2 mcb either side.
Cooker/shower on left
Lights/sockets on right
So the power to the shower switch is fine, again this can function fine and send power to the shower, bit as soon as the shower is pressed is wipes both rcds straight out after 2seconds.
I did a insulation resistance test, was getting 0.25megohms.
Removed tge switch and was getting 459megohms. So thought new switch, put new switch on and still wiping the whole board out, but obviously were not getting a dead short as the power to the shower is fine untill pressed.
Quite interesting this one. But such a obvious one which I will always look out for on my future PIRs