Had a call out late last night, everytime the shower comes in it's blows the whole house.

The set up of the board is duel rcd. 2 mcb either side.

Cooker/shower on left

Lights/sockets on right



So the power to the shower switch is fine, again this can function fine and send power to the shower, bit as soon as the shower is pressed is wipes both rcds straight out after 2seconds.

I did a insulation resistance test, was getting 0.25megohms.
Removed tge switch and was getting 459megohms. So thought new switch, put new switch on and still wiping the whole board out, but obviously were not getting a dead short as the power to the shower is fine untill pressed.

Quite interesting this one. But such a obvious one which I will always look out for on my future PIRs
 
To be fair I had bought one for ÂŁ60 a protek one and that seemed ok, are they anygood?

Also just installed a Chint one which was apparently "ip" rated so could take top entry without sealing "according to wholesaler"

But your right screwfix (elecfix) have mk ones on offer at mo ÂŁ50 + vat and that's with the breakers.
 
Not necessarily, if there's a route back via another circuits neutral (under fault conditions) the rcd will trip if the imbalance L->N is in excess of the rating (nominal 30mA).
Someone was also postulating about the posibility of an induced current from one RCBO to an adjacent RCBO causing a trip (must be very poorly designed if that's the case though).
 
Last edited:
Lol, but soon as that shower draws it's power then surely this would be able to cause say a 2nm jump to the next bus bar? Or would it! I don't kno, I bin at it for only 7 years, but my mate i work with has been at it 49 years and he gas never saw this, he couldn't even explain why.
 
With it being dark they may have been a small raggy stray bit of copper which you overlooked ( been late and dark etc... ), busbars were close enough for a little peice to touch the other, you snipped the bar back and its solved the problem
 
Lol, but soon as that shower draws it's power then surely this would be able to cause say a 2nm jump to the next bus bar? Or would it! I don't kno, I bin at it for only 7 years, but my mate i work with has been at it 49 years and he gas never saw this, he couldn't even explain why.
It would only jump if there's a PD to make it.
 

Reply to Guess the fault in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
989
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top