sure - do you mean the boiler label (below)?

I WAS TOLD THIS PCB IS NEW!! I paid £250 for it... did the guy rip me off bringing me a used one??

View attachment 100150
The white flex appears to be connected in all the right places, albeit sub-standardly.
I would turn the heating and hot water to the off position and then check to see if there is any voltage between neutral and the grey wire. The boiler and pump should only fire up when there is a demand for either heating or hot water or frost protection situation, which is highly unlikely at the moment, due to all the glorious sunshine.
 
OK, just bought a meter.

V~ 200 and on 4 and 3?

I just loaded a manual from Google instead of their website and it looks more like yours. It appears that it doesn't accept any switched live but expects a switched signal between 3 and 4. The orange and grey cores are the switched ones from the valves and could be used for that.

Do you have a meter to test that there is 230v on terminal 4?
 
The white flex appears to be connected in all the right places, albeit sub-standardly.
I would turn the heating and hot water to the off position and then check to see if there is any voltage between neutral and the grey wire. The boiler and pump should only fire up when there is a demand for either heating or hot water or frost protection situation, which is highly unlikely at the moment, due to all the glorious sunshine.
Hi, thanks

ok, so on the meter V~ 200 and on the blue (N) and grey wire (4) on the PCB?

Thank you
 
Yes - heating and hot water being off (on the Nest)!
I would now test between neutral and brown of both of your zone valves when heating and hot water is still in the off position. Hopefully you won’t have 230 volts there. I would then separate the oranges on your zone valves and measure between neutral and each of the oranges in turn to see if one of your zone valves has an issue. Could be a micro switch issue In one or both of your zone valves.
 
I would now test between neutral and brown of both of your zone valves when heating and hot water is still in the off position. Hopefully you won’t have 230 volts there.
I have 244V
I would then separate the oranges on your zone valves and measure between neutral and each of the oranges in turn to see if one of your zone valves has an issue.
They both have 244v

😳

any ideas?
 
If you have 244v between neutral and the terminal where your brown of the zone valves are connected in your wiring centre, when the heating and hot water are in the off position, then you have a problem possibly from the nest end.
I see...

So it could be the Nest's fault after all? (I spoke to Google who wants a "diagnostic" in order to send a replacement..)

Assuming you have seen the photo of the cabling at Nest? That seems correct?

Many thanks for your help!
 
I see...

So it could be the Nest's fault after all? (I spoke to Google who wants a "diagnostic" in order to send a replacement..)

Assuming you have seen the photo of the cabling at Nest? That seems correct?

Many thanks for your help!
You shouldn’t see 230v between neutral and brown when your heating and hot water are in the off position.
 
OK, so I checked again (my heart sunk before)

and

b/w Neutral and Brown on both ZV = 0v

b/w Neutral and Orange on both ZV = 244v

All while heating & HW OFF


Apologies, about the wrong info earlier...
 
I would remove the permanent live from the valves by disconnecting the orange from the top of 11 and move it to the spare of 5. The spare black looks like it goes to the boiler. I'd connect that to 5 in the junction box and connect the black to 3 in the boiler.
 
OK, so I checked again (my heart sunk before)

and

b/w Neutral and Brown on both ZV = 0v

b/w Neutral and Orange on both ZV = 244v

All while heating & HW OFF


Apologies, about the wrong info earlier...230v should only be present between neutral and orange when you select either heating or hot water after the valve has motored open
 

Reply to Heating Wiring Problem - cylinder thermostat not working in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

Similar threads

S
  • Article
Programmable digital cylinder stat I bought one of these: and I am using it to control the temperature of my hot tub, and it works great. Does...
Replies
0
Views
71
siricosm
S
Brilliant. Thanks Brian much appreciate the advice.
Replies
2
Views
233

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top