C

claret73

Evening Chaps...
Had a 2nd call out today to a relative (let's say they're a client) for a fault on the downstairs Sockets.

In a nutshell the downstairs sockets are tripping the RCD. Been there nearly all day & cannot fathom out what might be the cause?

So, the board is a 16th MCB Only. There is a 63A 30mA RCD between the meter & the Main Switch which protects all circuits. It is only the downstairs sockets tripping the RCD. The circuit concerned is 2x Rings into the MCB. 1 does 3x sockets in the front room, the 2nd does the dining room, kitchen & outside socket which runs out an armoured to a 2nd weatherproof box.

I disconnected the outside socket from the spurred cable in the dining room. Switched back on, still trips. Split out the circuits having done a continuity to find the 2x legs. Found out which was the tripping circuit & ignored the other. All Appliances were disconnected.

Tests I performed:
End to end to check continuity on Line & CPC
Line to CPC Insulation resistance
Ramp Test on the RCD

The board is boxed into a corner & the Neutral bar is very difficult to get access to, so was not too happy with taking out the Neutral connections.
However I reconnected the circuit & did L-CPC, N-CPC & L-N Insulation resistance.

The meter read >99.9 (Megger MFT) & so all Cables were deemed OK?
Took all sockets concerend off & checked for nicks/damage & tightness of the terminals. All OK...

So I don't know what the problem is? It's still tripping. I put the other Ring back in to give them some power.

Any ideas what I may have glaringly missed??? Any help greatly appreciated...
Thanks
Andy
 
Do you have a clamp meter at your disposal? If so I'd be tempted to try and confirm your suspicion about the RFC using that (and eliminate the other circuits as well if possible). As the RCD is before all of the circuits you are probably dealing with a combination of leakage faults. You have a ramp test from the RCD so you'll know what it's tripping threashold is.
 
Thanks again Lads! Going back on Friday...Not got a clamp meter to hand...(Ahem!)
Got a call today to go look at another fault job, tripping MCB on a lighting circuit!! Ohhhh Nooooo! It's really not my forté...
 
It sounds to me like a nuetral. I'd IR test the whole shooting match at the DB then disconnect that outside pir/light thingy. If that doesnt sort it then its testing all the circuits in a methodical manner at the DB.
Best of luck.
 
Well Guys, went back to this yesterday. Decided to dead test at the board again in case I'd missed something. With it all connected & dead proceeded with IR Tests again on each circuit. All Perfect...So, bit the bullet & 1 by 1 started disconnecting the sockets. Narrowed it down to a spur from a JB which was feeding the dishwasher. This cable was inaccessible as it was jointed above the ceiling. Tracing it back I could just see it clipped behind the sink unit level with the floor on the outside wall. Either it's a fault at the JB which I can't get to or being on the outside wall is susceptible to the damp conditions??? Anyhow, with that out of circuit I managed to power it back up...

Just really glad it was a non costly fault for them in the end...Pain in the A**E! Though...
So Thanks for all the help here for everybody who replied...
 

Reply to Help required with a Domestic Ring Final fault in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
644

Similar threads

  • Question
At this "first" fitting it's loop in. The rest appear to be joint boxes and old par 38 light fittings. It is reasonably old wiring but not...
Replies
3
Views
363
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top